APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:48 AM . Last Modified: 2024-03-15 05:47 AM
Hi,
trying to update the firmware of my new model SMT750RMI2UC. First i tested powernet431.mib which failed twice, then i tested powernet404.mib - also failure.
Isn´t this the correct firmware file for my model? - i found those file through filtering the available firmwares by selecting this model.
I am connected to the APC through Web (additional Network card is attached to APC) - same LAN (no VLANs), 100 MBit for APC, 1Gbit for my Notebook.
Log says:
12/19/2019 | 00:15:54 | Device | UPS: Firmware transfer to UPS failed |
12/19/2019 | 00:15:54 | Device | UPS: Finished UPS firmware transfer [Timeout] |
Thanks,
Phil
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:48 AM . Last Modified: 2024-03-15 05:47 AM
Hi,
The powernet mib is not firmware. The mib is a file used with SNMP. Are you attempting to upgrade the firmware for the UPS or for the network management card.
If you want to update the firmware on the network card the latest firmware will be found here. https://www.apc.com/shop/us/en/products//P-SFSUMX680
If you want to update the firmware on the SMT750RMI2UC you will find that at this link. https://schneider-electric.box.com/s/vq7tb93ikp1fvwt9x6oi9fck47c5m6zk
Before upgrading the UPS firmware be sure to read the instructional PDF. Note: when the UPS firmware is updated the output power will be cut so all attached equipment should be powered of prior to the upgrade.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:48 AM . Last Modified: 2024-03-15 05:47 AM
Hi,
The powernet mib is not firmware. The mib is a file used with SNMP. Are you attempting to upgrade the firmware for the UPS or for the network management card.
If you want to update the firmware on the network card the latest firmware will be found here. https://www.apc.com/shop/us/en/products//P-SFSUMX680
If you want to update the firmware on the SMT750RMI2UC you will find that at this link. https://schneider-electric.box.com/s/vq7tb93ikp1fvwt9x6oi9fck47c5m6zk
Before upgrading the UPS firmware be sure to read the instructional PDF. Note: when the UPS firmware is updated the output power will be cut so all attached equipment should be powered of prior to the upgrade.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.