Hello
One of my UPSs (Smart-UPS SRT 6000) stopped the output power suddenly, log of UPS is attached, appreciate your assistance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:19 AM . Last Modified: 2024-03-07 11:13 PM
Inverter faults don't tend to be fixable but you could try to dead brain the UPS but that will only help if the UPS is detecting a fault that doesn't exist.
https://www.apc.com/ie/en/faqs/FA156611/
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:19 AM . Last Modified: 2024-03-07 11:13 PM
It looks like there is an inverter fault with your UPS:
02/07/2021 13:18:19 Device UPS: An inverter fault exists. 0x0165
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:19 AM . Last Modified: 2024-03-07 11:13 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:19 AM . Last Modified: 2024-03-07 11:13 PM
Thank you Gavan for replying.
it is something I can fix my self by performing some troubleshooting procedure, or I have to log a call for professional service?
Note: the unit is out of warranty.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:19 AM . Last Modified: 2024-03-07 11:13 PM
Inverter faults don't tend to be fixable but you could try to dead brain the UPS but that will only help if the UPS is detecting a fault that doesn't exist.
https://www.apc.com/ie/en/faqs/FA156611/
-Gavan
Link copied. Please paste this link to share this article on your social media post.