Hello,
I’ve a used AP9617 and for the last 2 weeks I'm desperately trying to connect to it…
After reading here about limited functionality of the ‘reset’ button on AP9617,
I bought CrossOver Adapter and was able to find AP9617 IP address.
The IP address is pingable but I can’t get to the web page. I always get ‘The connection has timed out’
P.S. I'm using this NMC card in SUA1000
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 11:38 AM . Last Modified: ‎2024-03-15 04:53 AM
Hi Alex,
If you read the article it describes how to use the console port to by pass the password, you don't need access to the settings. Then once the password is reset you can change any other settings via the CLI.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 11:38 AM . Last Modified: ‎2024-03-15 04:54 AM
Hi Alex,
Try following the procedure for the NMC1 in the link below:
https://www.apc.com/us/en/faqs/FA156075/
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 11:38 AM . Last Modified: ‎2024-03-15 04:54 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 11:38 AM . Last Modified: ‎2024-03-15 04:54 AM
Gavan, thank you for the help, but i'm not sure how that procedure helps if i can't get to the settings...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 11:38 AM . Last Modified: ‎2024-03-15 04:53 AM
Hi Alex,
If you read the article it describes how to use the console port to by pass the password, you don't need access to the settings. Then once the password is reset you can change any other settings via the CLI.
-Gavan