Errors "Managed PC shutdown not provided" and "APC UPS Service not running"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Errors "Managed PC shutdown not provided" and "APC UPS Service not running"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:06 AM . Last Modified: ‎2024-03-13 01:46 AM

0 Likes
3
4563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:06 AM . Last Modified: ‎2024-03-13 01:46 AM

Errors "Managed PC shutdown not provided" and "APC UPS Service not running"

I see the error messages "Managed PC shutdown not provided" and "APC UPS Service not running". If I run a Self-test, the unit passes. I have a Back-UPS ES 750. I use PowerChute Personal Edition 3.0.2. My computer runs Windows 10 Home. I read a response in this forum from 2009 that advised to set the Data Service and the UPS service to Automatic Start. I checked. The services were already marked Start. The PowerChute personal has the same error on my Win10 admin account as my Win10 user account. What do you suggest that I do to fix this? Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • back-ups
  • error
  • messages
  • PowerChute
  • service
  • shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:07 AM . Last Modified: ‎2024-03-13 01:46 AM

0 Likes
0
4560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:07 AM . Last Modified: ‎2024-03-13 01:46 AM

Hey APC,

I've a new Dell XPS desktop and I'm finding the latest version of PowerChute Personal 3.1.0 pulled from APCs site is not loading properly with an error as shown in this message's subject line.  Running the two command prompts you suggested previously, you can see what I'm getting.  Fails to start.  See attached. 

pGtsJTZIQYvhcRLwiqrz8g%3D%3D.pngpGtsJTZIQYvhcRLwiqrz8g%3D%3D.png

The computer came with McAfee Personal Security preloaded that I'm using for the 1yr service offered.  When I look at its activity report, I'm seeing repeated incoming network connection blocking entries that I'm thinking may be from the UPS I'm using, an older ES750.  See attached.

P6L%2BpTsG2v4UlCHFJEZxtA%3D%3D.pngP6L%2BpTsG2v4UlCHFJEZxtA%3D%3D.png

Do you have any suggestions of how I can get the managed pc shutdown service running?  It appears the blocked connection is coming from the same device but through varying ports.  I have snooped around McAfee and I can't really find a way to open up this connection, assuming this is the problem.  Any help would be appreciate.  Thanks.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:07 AM . Last Modified: ‎2024-03-13 01:46 AM

0 Likes
0
4561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:07 AM . Last Modified: ‎2024-03-13 01:46 AM

Hi,

IS the APC UPS Service running? You can check the status using the command prompt. The command is sc query "apc ups service" 

If the service is running you will get the reply shown below

If it is stopped restart it. The command is net start "apc ups service" Once started check the status using the earlier command. Once the apc ups service is running you will need to start the data server. The command is net start "apc data service"

If the service will not start I will need system information to troubleshoot. What if any malware and virus protection applications are running? 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:07 AM . Last Modified: ‎2024-03-13 01:46 AM

0 Likes
0
4561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:07 AM . Last Modified: ‎2024-03-13 01:46 AM

Well, this is embarrassing. When I first logged on this morning, the APC tray icon still had the ! on it. I ran the command as instructed. It showed exactly what it should. I looked at the APC tray icon and it was clean. No problem.

I am running Malwarebytes Corporate (1.80.1.1011) version and Bitdefender Antivirus Plus 2016

I may be writing back too soon. I suspect the problem will return. If so, I'll be back.

Thanks for the help.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:07 AM . Last Modified: ‎2024-03-13 01:46 AM

0 Likes
0
4561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:07 AM . Last Modified: ‎2024-03-13 01:46 AM

Hey APC,

I've a new Dell XPS desktop and I'm finding the latest version of PowerChute Personal 3.1.0 pulled from APCs site is not loading properly with an error as shown in this message's subject line.  Running the two command prompts you suggested previously, you can see what I'm getting.  Fails to start.  See attached. 

pGtsJTZIQYvhcRLwiqrz8g%3D%3D.pngpGtsJTZIQYvhcRLwiqrz8g%3D%3D.png

The computer came with McAfee Personal Security preloaded that I'm using for the 1yr service offered.  When I look at its activity report, I'm seeing repeated incoming network connection blocking entries that I'm thinking may be from the UPS I'm using, an older ES750.  See attached.

P6L%2BpTsG2v4UlCHFJEZxtA%3D%3D.pngP6L%2BpTsG2v4UlCHFJEZxtA%3D%3D.png

Do you have any suggestions of how I can get the managed pc shutdown service running?  It appears the blocked connection is coming from the same device but through varying ports.  I have snooped around McAfee and I can't really find a way to open up this connection, assuming this is the problem.  Any help would be appreciate.  Thanks.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore