Error when using snmpset with APC Switched Rack PDU
  • Error when using snmpset with APC Switched Rack PDU
Posted: ‎2021-07-09 04:20 AM . Last Modified: ‎2024-02-14 11:03 PM
1441
Hello, I have two types of APC switched rack PDU, Model AP7920, and the newer AP7920B units. I'm using snmp to control the outlet power under Ubuntu.
B-DoubleE_apc
Commander B-DoubleE_apc
Commander
Hi Andrew,
The rPDU2 tree is not compatible with the older model NMC1, the older model rPDU's that use our 1st generation NMC have been discontinued. You would need to use two different OID's depending on which model PDU you are using.
B-DoubleE_apc
Commander
Hi Andrew,
The AP7920B is built with on our NMC2 platform, and uses the same hardware and firmware revisions as the AP8xxx series. As such, it will use the same section of the MIB as the AP8xxx, called "rPDU2". The OID to use for controlling outlets is .1.3.6.1.4.1.318.1.1.26.9.2.4.1.5, titled "rPDU2OutletSwitchedControlTable"
Hi Matt,
Thank you.
I used rPDU2OutletSwitchedControlCommand and it works without an error now.
Is it possible to update the firmware on the older units, or do I have to use two different commands depending on which PDU I'm using?
B-DoubleE_apc
Commander
Hi Andrew,