Hello, I have two types of APC switched rack PDU, Model AP7920, and the newer AP7920B units. I'm using snmp to control the outlet power under Ubuntu.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:20 AM . Last Modified: 2024-02-14 11:03 PM
Hi Andrew,
The rPDU2 tree is not compatible with the older model NMC1, the older model rPDU's that use our 1st generation NMC have been discontinued. You would need to use two different OID's depending on which model PDU you are using.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:20 AM . Last Modified: 2024-02-14 11:03 PM
Hi Andrew,
The AP7920B is built with on our NMC2 platform, and uses the same hardware and firmware revisions as the AP8xxx series. As such, it will use the same section of the MIB as the AP8xxx, called "rPDU2". The OID to use for controlling outlets is .1.3.6.1.4.1.318.1.1.26.9.2.4.1.5, titled "rPDU2OutletSwitchedControlTable"
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:20 AM . Last Modified: 2024-02-14 11:03 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:20 AM . Last Modified: 2024-02-14 11:03 PM
Hi Matt,
Thank you.
I used rPDU2OutletSwitchedControlCommand and it works without an error now.
Is it possible to update the firmware on the older units, or do I have to use two different commands depending on which PDU I'm using?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:20 AM . Last Modified: 2024-02-14 11:03 PM
Hi Andrew,
The rPDU2 tree is not compatible with the older model NMC1, the older model rPDU's that use our 1st generation NMC have been discontinued. You would need to use two different OID's depending on which model PDU you are using.