Posted: 2021-07-08 12:13 AM
This was originally posted on APC forums on 4/1/2015
Model Number: | AP9630 |
what I am trying to achieve is to turn off the server when there is a power outage.
Posted: 2021-07-08 12:13 AM
This reply was originally posted by Bill on APC forums on 5/26/2015
Phil,
For PowerChute Network Shutdown to communicate with the Network Management Card the user name and authentication phrase must match. The password is unique to PCNS and does not need to match the NMC.
Posted: 2021-07-08 12:13 AM
This was originally posted on APC forums on 5/26/2015
Make sure the username and password you assign to the PowerChute Network Shutdown app is identical to the following three items on the management card:
Posted: 2021-07-08 12:13 AM
This reply was originally posted by Bill on APC forums on 5/26/2015
Phil,
For PowerChute Network Shutdown to communicate with the Network Management Card the user name and authentication phrase must match. The password is unique to PCNS and does not need to match the NMC.