Posted: 2021-07-08 12:13 AM . Last Modified: 2024-02-29 11:28 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:13 AM . Last Modified: 2024-02-29 11:28 PM
| Model Number: | AP9630 |
what I am trying to achieve is to turn off the server when there is a power outage.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:13 AM . Last Modified: 2024-02-29 11:28 PM
Phil,
For PowerChute Network Shutdown to communicate with the Network Management Card the user name and authentication phrase must match. The password is unique to PCNS and does not need to match the NMC.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:13 AM . Last Modified: 2024-02-29 11:28 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:13 AM . Last Modified: 2024-02-29 11:28 PM
Make sure the username and password you assign to the PowerChute Network Shutdown app is identical to the following three items on the management card:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:13 AM . Last Modified: 2024-02-29 11:28 PM
Phil,
For PowerChute Network Shutdown to communicate with the Network Management Card the user name and authentication phrase must match. The password is unique to PCNS and does not need to match the NMC.
Link copied. Please paste this link to share this article on your social media post.