Error registering with the Network Management Card(s).

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Error registering with the Network Management Card(s).
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

0 Likes
7
9494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

Error registering with the Network Management Card(s).

Hello Community,

I'm trying to configure PowerChute on vMA in order to shutdown virtual machines on vmware.

After installing PowerChute, I'm starting setup wizard and getting in trouble:

The Error message: PowerChute is not receiving data from the Network Management Card.

I've already checked all this options, but nothings resolve the issue.

  1. Verify that the Administrator Username and AuthenticationPhrase are the same for PowerChute and the NMC.
  2. Verify that UDP port 3052 is not being blocked by a firewall.
  3. Check the IP settings on the PowerChute machine and on the NMC user interface to verify that the default gateway and subnet mask are correct.
  4. Update the firmware on the NMC to the latest version which can be downloaded from the APC Web site, or contact APC Customer Support.

In the PowerChute logs I can see:

TimeIP addressDescription
14:21:18 x.x.x.31 Waiting for Network Management Card response.
14:21:18 x.x.x.31 Registering x.x.x.35 http://x.x.x.31:80.
14:21:18 x.x.x.31 Connected to Network Management Card.
14:21:18 x.x.x.31 Checking connection to http://x.x.x.31:80

The UPS Network Management Card is  AP9631

Please help

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9631
  • NMC
  • PowerChute
  • vma
  • vmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

0 Likes
0
9488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

Hi,

Where these errors logged after you followed the steps to add the IP address manually and started PCNS and are you running PCNS 3.1 on vMA 5.5? The errors indicate that PCNS is not receiving any packets from the NMC. Would you provide the pcnsconfig.ini file and the NMC config.ini file.

If your not comfortable providing the info through the forum you can contact local technical support http://www.apc.com/site/support/index.cfm/contact-information/ and they will be glad to help you.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

1 Like
1
9489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

Hi. I had exactly the same issue. Turns out (on my system at least) when the install adds the Windows Firewall Rules it only adds them to the public network. I went into the Firewall settings and changed it to apply the rules to the Domain Network and it worked perfectly.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

0 Likes
0
9489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

Hi,

I am getting the same error, but not with a VM. I have installed this with no problem on several servers, but for some reason it won't register with this one server. I have tried all the same steps to resolve the issue, but nothing has worked. The weird thing is I know its talking to the Network Management Card because when I go into the card directly under PowerChute Network Shutdown Clients it shows the IP of the server failing to register.

However, when I am going through the cfg wizard to register this server no matter what I try I always get the following.

The Error message: PowerChute is not receiving data from the Network Management Card.

I would also appreciate some troubleshooting assistance.

Thanks,

Bob

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:25 AM

0 Likes
0
9489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:25 AM

Hi,

I assume you are installing PCNS 3.1 on vMA 5.5.

PCNS uses port 80 when registering with the NMC so you need to verify that port 80 is open. If it is then I suggest manually registering PCNS with the card. First stop PCNS daemon on the vMA. The command is sudo /etc/init.d/PowerChute stop. Then go to /opt/APC/PowerChute/group1 (this is assuming you installed to the default path) and edit pcnsconf.ini You should enter the ip address of the NMC, change enrolwithNMC to false, and enter the user name and password. NOTE: user name and password entries need to be added completely as they are not saved in the ini file and will be deleted once the daemon is restarted.

Example:

[NetworkManagementCard]
mode = single
IP_1 = (NMC IP address)
port = 80
protocol = http
enrolWithNMC = false
username = (must match NMC)
password = (your choice)
acceptCerts = false

 

Also, under the section for [Networking] enter the ip address of the vMA
Example:
localHostAddress = 192.168.1.100

Then log onto the NMC and under the PowerChute section add the IP address of the vMA. After adding the vMA IP address to the NMC log back into the vMA and restart PCNS sudo /etc/init.d/PowerChute start.

You should then be able to log into PCNS web interface on the vMA using the user name and password enter earlier and complete the setup. Once the setup is completed you should stop PCNS again, change enrolWithNMC back to true and then restart PCNS. If in the event log you get an error stating the “Security information for http://x.x.x.x:80 is incorrect.” go to communication settings and enter the authentication phrase and click apply.

If you are still having an issue have entering the IP address manually look in /opt/APC/PowerChute/group1/error.log It should list what the cause of the communication issues are.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:25 AM

0 Likes
0
9489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:25 AM

Thanks for your reply,

here is the error I'm receiving in log (/opt/APC/PowerChute/group1/error.log)

ERROR pool-1-thread-8 com.apcc.pcns.datagramservice.DatagramTask - java.net.SocketTimeoutException: Receive timed out
ERROR pool-1-thread-8 com.apcc.pcns.datagramservice.DatagramTask - java.net.SocketTimeoutException: Receive timed out
ERROR pool-1-thread-8 com.apcc.pcns.datagramservice.DatagramTask - java.net.SocketTimeoutException: Receive timed out
ERROR pool-1-thread-8 com.apcc.pcns.datagramservice.DatagramTask - java.net.SocketTimeoutException: Receive timed out
ERROR Thread-2 com.apcc.m11.components.StdPowerSource.EventRules.OverloadStatusRule - com.apcc.m11.arch.CommunicationException
ERROR Thread-2 com.apcc.m11.components.StdPowerSource.EventRules.PowerSourceTurnOffInitiatedRule - com.apcc.m11.arch.CommunicationException

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

0 Likes
0
9489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

Hi,

Where these errors logged after you followed the steps to add the IP address manually and started PCNS and are you running PCNS 3.1 on vMA 5.5? The errors indicate that PCNS is not receiving any packets from the NMC. Would you provide the pcnsconfig.ini file and the NMC config.ini file.

If your not comfortable providing the info through the forum you can contact local technical support http://www.apc.com/site/support/index.cfm/contact-information/ and they will be glad to help you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

0 Likes
0
9489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

Thanks for the Help.

But I downloaded a PCNS as an .OVA and deployed it on vmware, after that the communication works perfect!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

1 Like
1
9490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

Hi. I had exactly the same issue. Turns out (on my system at least) when the install adds the Windows Firewall Rules it only adds them to the public network. I went into the Firewall settings and changed it to apply the rules to the Domain Network and it worked perfectly.

Reply

Link copied. Please paste this link to share this article on your social media post.

premax
premax
Cadet

Posted: ‎2021-09-21 02:27 AM

In response to Anonymous user
0 Likes
0
9334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-21 02:27 AM

Thank you for the public firewall hint. Worked for me too.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore