Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
Smart-UPS RT 5000 XL 12 seconds remaining Time
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-1706:30 AM
Smart-UPS RT 5000 XL 12 seconds remaining Time
Hello,
we have a Smart-UPS RT 5000 XL with two Batteries. the Batteries are (thats what the Website says) at 100% charge. The UPS has a load of 65% but it tells it will last 12 seconds when power goes down.
We unplugged some devices, had in bypass and back and started a calibration nothing changed. We had no window for a maintainance so that we could reboot it.
I guess we have to change the Batteries? or could a boot help? there are only discharged battery messages in the log.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-2011:02 AM
@Anonymous user
It sounds like the batteries need to be replaced. How old are the batteries and what is the environment the UPS is in?
An RT5000XL uses the RBC140. That battery pack includes two strings. Each string is 8 x 12v batteries. A good 12v battery should have a float voltage of 13.5v DC. At 13.5v * 8 = 108v. if the voltage is less that would indicate weak battery or batteries.