Hi,
after a battery replacement on a Smart-UPS RT 5000 XL, we can't access to the web gui anymore, with the error in subject.
The about result:
E000: Success
Hardware Factory
---------------
Model Number: AP9631
Serial Number: 5A1405T14XXX
Hardware Revision: 05
Manufacture Date: 02/01/2014
MAC Address: 00 C0 B7 A1 D5 23
Management Uptime: 290 Days 20 Hours 21 Minutes
Application Module
---------------
Name: sumx
Version: v6.0.6
Date: Apr 5 2013
Time: 11:25:39
APC OS(AOS)
---------------
Name: aos
Version: v6.0.6
Date: Apr 5 2013
Time: 10:36:37
APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.2
Date: Jan 21 2010
Time: 13:35:57
What i can do to fix the web gui without any power outage?
Ty
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-14 01:24 PM
@Anonymous user
You are running old NMC firmware. You should upgrade to the latest. Here is a link to FAQ that discusses upgrading the firmware.
http://www.apc.com/us/en/faqs/FA156047
here is a link to the download site for the latest firmware.
https://schneider-electric.app.box.com/s/9dyoxlmiojfq1mdqj9d1ae9bn9fe9wmb
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-20 01:08 AM
Hi,
the NMC Firmware update utility return me "resume not supported for scp transfers" error on scp... and can't connect to ftp.
Ftp is enable, checked via cli:
apc>ftp
E000: Success
Service: enabled
Ftp Port: 21
Manual scp return in a stuck transfer with 0 byte for second...
We also tried a reset of configuration with network preservetion, with no result.
Looking at the FS:
apc>dir
E000: Success
2784512 Apr 5 2013 apc_hw05_aos_606.bin
0 Feb 1 2014 db/
0 Feb 1 2014 ssl/
0 Feb 1 2014 ssh/
0 Feb 1 2014 logs/
0 Feb 1 2014 sec/
0 Feb 1 2014 dbg/
0 Feb 1 2014 fwl/
0 Feb 1 2014 email/
0 Feb 1 2014 lang/
0 Feb 1 2014 upsfw/
0 Feb 1 2014 rms/
0 Feb 1 2014 scg/
also the eventlog fail:
apc>eventlog
E100: Command Failed
Event Log Not Available
and the logs are stuck in the date when we replace the battery:
apc>cd logs
E000: Success
apc>dir
E000: Success
0 Feb 1 2014 ./
0 Feb 1 2014 ../
80896 Oct 21 2020 event.txt
23552 Oct 21 2020 data.txt
1 Feb 1 2014 dlogmask
any suggestion?
ty
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-20 08:59 AM
@Anonymous user
What version of the firmware are you attempting to load? The latest is 6.9.6 and can be downloaded from https://www.apc.com/us/en/faqs/FA410359/
As for the failure, have you tried to manually ftp the file/s to the NMC? See Schneider Electric FAQ FA156047 for instructions.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.