Entry Level UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Entry Level UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:50 PM . Last Modified: ‎2024-03-14 01:15 AM

0 Likes
7
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:50 PM . Last Modified: ‎2024-03-14 01:15 AM

Entry Level UPS

I am looking for an entry level UPS that is both compatible with Windows Server 2003/2008 and communicates via USB to be used in a single server application. Is the SMT750 my only option?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:51 PM . Last Modified: ‎2024-03-14 01:15 AM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 PM . Last Modified: ‎2024-03-14 01:15 AM

10-20 min runtime
clone (no brand name) running windows server 2003
~$150-$250 price range

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:50 PM . Last Modified: ‎2024-03-14 01:15 AM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:50 PM . Last Modified: ‎2024-03-14 01:15 AM

Is it more like a desktop that's been converted into a server? You might be able to get away with a Back-UPS model, though it depends on the power supply - most server power supplies don't like the longer transfer times the Back-UPS have, which is why the typical recommendation for a server is a Smart-UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:50 PM . Last Modified: ‎2024-03-14 01:15 AM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:50 PM . Last Modified: ‎2024-03-14 01:15 AM

I am looking for an entry level UPS that is both compatible with Windows Server 2003/2008 and communicates via USB to be used in a single server application. Is the SMT750 my only option?

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:51 PM . Last Modified: ‎2024-03-14 01:15 AM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 PM . Last Modified: ‎2024-03-14 01:15 AM

What is the Power Consumption(Watts) of the total system?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:51 PM . Last Modified: ‎2024-03-14 01:15 AM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 PM . Last Modified: ‎2024-03-14 01:15 AM

not sure what the power consumtion is. it is a basic clone pc with 300watt power supply, 1 internal sata drive with 4GB of ram running Server 2003. its a very basic server used for file sharing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:51 PM . Last Modified: ‎2024-03-14 01:15 AM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 PM . Last Modified: ‎2024-03-14 01:15 AM

I agree with Buzz comments. If your system power supply has got an active PFC supply, then I recommend you to go for any one of the APC Smart UPS SUA,SMT or SMX UPSs. You can go for SMT750 or you may check out the Coastal Business Machines direct sales of refurbished APC UPS systems.

You can purchase the SUA1500 UPS for $ 199.00 from CBM. All Certified Pre-Owned UPS systems are tested to the same specifications as our brand new products. All Certified Pre Owned UPS systems come with a one year warranty and free technical support directly from Coastal Business Machines.

Coastal Business Machines offers both telephone and web based sales options. You may reach Coastal Business Machines by telephone by calling 800 2 FIX UPS (800-234-9877), Monday through Friday from 8am until 8pm EDT. You may also explore your options directly through the Coastal Business Machines website, linked below:

http://www.buyUPSonline.com

As an added bonus, CBM is offering a $5 WEB ONLY discount off of the online purchase of any refurbished UPS when you use the promotion code "CPOBT07F6".

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:51 PM . Last Modified: ‎2024-03-14 01:15 AM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 PM . Last Modified: ‎2024-03-14 01:15 AM

Also, just because you have a PFC power supply doesn't mean you need a Smart-UPS. There's a risk for overkill, though it's the "safest" route. Basically you just have to keep in mind the info in this kbase.

I have a 600w PFC power supply in my gaming desktop and it's connected to a BR800BLK, works like a charm. The PC doesn't really pull more than 300-400w max.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:51 PM . Last Modified: ‎2024-03-14 01:15 AM

0 Likes
0
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:51 PM . Last Modified: ‎2024-03-14 01:15 AM

10-20 min runtime
clone (no brand name) running windows server 2003
~$150-$250 price range

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore