Hi,
Probably a simple question to answer..
I've got a Matrix-UPS 5000 and have 4 Smartcell XRs connected to it. My EU LED indicates "*01 Battery Packs Need Replacement*".
How can I tell which battery of the four needs replacing?
Thanks,
Peter
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:51 PM . Last Modified: 2024-03-14 01:15 AM
You have 4 separate Smartcell-XR frames? Or do you mean one XR frame that contains 4 batteries? If you have 4 frames, you can tell which one needs a battery based on the red LED indicator on the front of the frame. Otherwise, if it's one XR frame, you should replace all 4 of the batteries - RBC14 - like Nix said.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:51 PM . Last Modified: 2024-03-14 01:15 AM
Normally you should better replace the whole set - since they are all on one DC Bus and it would give you some imbalance if you just replaced one, that might result in a shorter lifespan for the replacements.
You can also check the serial # of your 4 SmartCell XRs - if they are close together it might also be an indicator that more than one is from the same datecode and might need replacing.
The good thing is: the RBC14 Battery Set is still available and would be the replacement kit for 1 XR Frame:
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=RBC14
The bad thing: the Smartcell-XR Frames have a battery communications card which could also be faulty resulting in false errormessages. Since the whole matrix UPS Range and its parts have reached End of Life / End of Support Beginning this year (the UPSs themselves even earlier) those cards are no longer available as a replacement.
I would personally highly recommend using the Trade-UPS Program to get an SURT Range unit for your solution.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:51 PM . Last Modified: 2024-03-14 01:15 AM
You have 4 separate Smartcell-XR frames? Or do you mean one XR frame that contains 4 batteries? If you have 4 frames, you can tell which one needs a battery based on the red LED indicator on the front of the frame. Otherwise, if it's one XR frame, you should replace all 4 of the batteries - RBC14 - like Nix said.