Hi Denis,
Modbus is not natively supported on a SURTD model UPS. You would need to purchase a smart-slot accessory, the AP9630/31/35 network management card. The AP9630/31 have support for Modbus TCP (as of firmware rev v6.4), and the AP9635 supports Modbus TCP and RTU (also as of firmware rev v6.4).