Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

Email Notification Configuration problems

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Email Notification Configuration problems
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
shortstop20_apc
Crewman shortstop20_apc
Crewman

Posted: ‎2021-07-01 05:13 AM

0 Likes
11
1564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:13 AM

Email Notification Configuration problems

This was originally posted on APC forums on 2/12/2014


Hello,

We have about 100 APC UPS devices here on campus. All are monitored using Network Management cards. Some are older versions, some are newer, so they have a mix and match of firmware as well.

Recently, after updating all of the "UPS Network Management Card 2" cards on campus to  v6.0.6 I noticed my email notifications sent from cards running v6.0.6 showed the sender as my email address. Older cards running v3.7.2 are still sending out Notification Emails as normal, they use the email address I specify under "From Address".

Here's the configuration I am using on all cards, regardless of software version.

DNS server is the same on all cards.

From Address: *Name-of-UPS@ourdomain.com*    <-------------This is what I should see as the "From" address when I receive a notification from the UPS, I'm seeing my email address instead.

SMTP Server: *hostname of our email server*

Port: 25

No Authentication

Use SSL/TLS: Never

Require CA Root Certificate: Not enabled(unchecked)

Under the Recipients tab:

To Address: *myemailaddress@ourdomain.com*

Format: Long

Server: Recipient

No Authentication

Require CA Root Certificate: Not enabled(unchecked)

Any help is appreciated.

Thanks,

Joel

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:14 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:14 AM

This reply was originally posted by Angela on APC forums on 2/13/2014


No problem. And yes, I did confirm it and just entered a request to get it fixed.

Let me know if you need any more help.

See Answer In Context

Reply
Share
Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:13 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:13 AM

This reply was originally posted by Angela on APC forums on 2/12/2014


How did you configure the NMC2's for notifications - did you load a config.ini from an older card on to the new management card? Or configure these from scratch via the web?

It'd also be helpful to see a config.ini file, if possible, from both systems if you can. (Instructions here on how to download config.ini -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...)

Reply
Share
shortstop20_apc
Crewman shortstop20_apc
Crewman

Posted: ‎2021-07-01 05:13 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:13 AM

This was originally posted on APC forums on 2/12/2014


Yes, I did load a config.ini from an older card to the newer card. I suppose maybe that caused a glitch after I upgraded to v6.0.6 on the NMC2's.

I'll try to upload the configs later when I have a chance.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:13 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:13 AM

This reply was originally posted by Angela on APC forums on 2/13/2014


I am not sure but I might me able to tell when I see what config was loaded to the 6.0.6 NMC (which maybe some keywords or values are different) and then what the current config.ini is at least to see if we can fix it. Thanks!

Reply
Share
shortstop20_apc
Crewman shortstop20_apc
Crewman

Posted: ‎2021-07-01 05:14 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:14 AM

This was originally posted on APC forums on 2/13/2014


Thanks Angela,

Could I possibly PM or email the configuration files to you?

I'm hesitant to post them up on the public forum since I would be revealing IP Addresses of our DNS servers, my email address, etc.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:14 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:14 AM

This reply was originally posted by Angela on APC forums on 2/13/2014


Hi again,

Yes, you can remove any IP information if you'd like or I'll also send you an email offline so you can send the files that way.

Reply
Share
shortstop20_apc
Crewman shortstop20_apc
Crewman

Posted: ‎2021-07-01 05:14 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:14 AM

This was originally posted on APC forums on 2/13/2014


I replied to your email.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:14 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:14 AM

This reply was originally posted by Angela on APC forums on 2/13/2014


Thanks!

Hope you don't mind that I share one thing for those that see this thread. You informed me that what you did was:

Around a year ago I did a mass configuration on all devices(via APC INI utility) using the same config in order to get consistent configurations on all devices. At that time, all NMC/NMC2 were running the older software, version 3.

A few months ago, I updated all NMC2’s to v6.0.6 and that’s when I noticed that email notifications from these devices were not as they were before.

So for NMC1 v3.X.X and actually NMC2 was at v5.X.X but it was very similar to v3.X.X, many config.ini values and keywords were the same. For 6.0.6, it is another animal if you will and there are many differences.

One thing I wanted to make sure was known was as outlined here (Things To Consider When Upgrading or Downgrading a Network Management Card 2 (NMC2) Device between v...), when you upgrade to v6.X.X, there are a few issues. 1.) The SMTP server info gets ported over incorrectly unfortunately and 2.) By design, the email notification events, intervals, frequency, etc are reset because it is not possible to keep them during the upgrade just because the firmwares are so different.

What I would recommend to ensure the most stability (theoretically anyway if there was not a problem currently) is to configure events the way you like it via the web on v6.0.6 then download that config.ini file with the correct syntax for v6.X.X and use that on your v6.X.X cards. Unfortunately, then we have this issue (Network Management Card 2 config.ini upload for event notification settings does not enable events i...) which is supposed to be fixed any day now with a v6.1.1 with the SMTP server info copying over wrong.

Going back to your original issue, I am going to look and see if I can replicate that I discovered you're using recipients mail setting which I know I don't test with often. We'll also see if we can get around having to use recipients mail setting and then I don't believe that issue will exist.

Reply
Share
shortstop20_apc
Crewman shortstop20_apc
Crewman

Posted: ‎2021-07-01 05:14 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:14 AM

This was originally posted on APC forums on 2/13/2014


Thanks Angela, that is helpful.

We have found that by entering email credentials under "Outgoing Mail Configuration" and changing the Server setting under Recipients to "Local" that the emails are then sent with the correct "From" address.

I'm still confused as to why this is needed on NMC2's and not NMC's though. The NMC's can send emails showing the correct "From" address without any credentials as well as using "Recipient" but the NMC2's cannot.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:14 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:14 AM

This reply was originally posted by Angela on APC forums on 2/13/2014


I have to think it's a bug. If I confirm I see the same behavior, I'll go ahead and log an issue on it for review.

Reply
Share
shortstop20_apc
Crewman shortstop20_apc
Crewman

Posted: ‎2021-07-01 05:14 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:14 AM

This was originally posted on APC forums on 2/13/2014


Thanks for your help Angela.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:14 AM

0 Likes
0
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:14 AM

This reply was originally posted by Angela on APC forums on 2/13/2014


No problem. And yes, I did confirm it and just entered a request to get it fixed.

Let me know if you need any more help.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc