ESXi 5 host not shutting down

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ESXi 5 host not shutting down
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:35 AM

0 Likes
3
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:35 AM

ESXi 5 host not shutting down

As per my subject, we have 3 ESXi 5 in HA environment, and was install vMA 5 with PCNS 3.0.1, below what had been done but not working.

My physical ESXi host ip = 10.10.10.12 & 10.10.10.13 & 10.10.10.14
My vMA 5 ip = 10.10.10.36

1, vifp addserver 10.10.10.12 -- Done
vifp addserver 10.10.10.13 -- Done
vifp addserver 10.10.10.14 -- Done

2, vifp listservers -- show result
10.10.10.12 ESXi
10.10.10.13 ESXi
10.10.10.14 ESXi

3, configure PCNS - Event --> On Battery --> Shutdown enable, delay 120 seconds -- Done

4, copy "shutdownvms.sh" file to vMA 5 in directory /opt/APC/PowerChute, run the command --> sudo chmod +x shutdownvms.sh

5, configure shutdown in PCNS --> run this command file --> shutdownvms.sh (download from APC to shutdown VMs in HA environment) -- Done

6, configure shutdown in PCNS --> command file need this many time to complete --> 180 seconds -- Done

7, modify the shutdownvms.sh script file --> hosts=(10.10.10.12 10.10.10.13 10.10.10.14)

8, add a line to shutdown file in directory /opt/APC/PowerChute/group1/bin come bundle with pcns301ESXi.tar.gz with this line -->
export PERL_LWP_SSL_VERIFY_HOSTNAME=0

The result of my testing is PCNS only able to shutdown vMA 5, not the VMs guest and ESXi host.
I'd test adjust the delay time longer but it still the same.
What could I missing in the setup? should I "chmod 744" and "chown root" to the script files? I was done this as well.
Anyone please help to advice?
Thank you.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 5
  • esxi
  • pcns
  • vma
  • vmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:35 AM

0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:35 AM

the answer is yes. you'll need to remove the host address from the script and from the server list.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:35 AM

0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:35 AM

hello,

i asked our PCNS team here for some help on this. here is what was suggested:

• Be sure that the servers have been added to the fasspass list. The command is vifptarget –s (example vifptarget -s 10.10.10.12)
• To verify there is communications between the vMA and the host/s, run the command vicfg-nics -– server -–list (example vicfg-nics -– server 10.10.10.12 -– list)

The list command should list all of the nics installed in the host. Once all hosts are added run the shut down test again.

Also, please verify what version of the vMA 5 is running i.e. 5.0, 5.0.0.1, 5.0.0.2?

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:35 AM

0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:35 AM

Hi, thank you for your response.
FYI, my vMA5 version is 5.0.0.2-724898.
If my VM in HA environment, can I just using the same method with the shutdownvms.sh script to test shutdown only single ESXi host instead all hosts?
Because my others ESXi host running under production.
Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:35 AM

0 Likes
0
1397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:35 AM

the answer is yes. you'll need to remove the host address from the script and from the server list.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore