Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Dual Power Source, Auto shutdown by AP9630
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0101:09 AM. Last Modified: 2024-03-0602:00 AM
Dual Power Source, Auto shutdown by AP9630
Hi, I plan to purchase two pcs of Smart 3k VA UPS for backing up one single server. They will be providing dual power source to my server. If I add the management card AP9630 to both UPS, can they communicate and auto shutdown the server once both UPS are out of battery? Thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0101:09 AM. Last Modified: 2024-03-0602:00 AM
Our Powerchute software has the ability to "listen" to multiple NMCs. During the install of powerchute network shutdown, you would select the option for "Redundant: Two or more UPS providing redundancy, with multiple power cables from the computer." You would then enter the IP info for each ap9630 and once able to communicate with each NMC, the install with go through as normal. The link below explains this as well. Let us know if you have any further questions
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0101:09 AM. Last Modified: 2024-03-0602:00 AM
Our Powerchute software has the ability to "listen" to multiple NMCs. During the install of powerchute network shutdown, you would select the option for "Redundant: Two or more UPS providing redundancy, with multiple power cables from the computer." You would then enter the IP info for each ap9630 and once able to communicate with each NMC, the install with go through as normal. The link below explains this as well. Let us know if you have any further questions