Double Conversion (Symmetra) and Surge Protection/EFI

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Double Conversion (Symmetra) and Surge Protection/EFI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:34 AM

0 Likes
9
1454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:06 AM . Last Modified: ‎2024-03-08 01:34 AM

Double Conversion (Symmetra) and Surge Protection/EFI

We are looking at purchasing: SYH6K6RMT-P1: APC Symmetra RM 6kVA Scalable to 6kVA N+1 208/240V w/208 to 120V Step-Down Transformer

I noticed the Symmetra (with Step-Down Transformer) doesn't claim to offer Surge Protection or filtering?

What is the best method to add this to a Symmetra UPS? OR is it not required because of the double conversion technology?

Or, is it just good practice to plug devices into surge protectors, then into the transformer (UPS) ?

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

0 Likes
0
1454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

Commercial Surge Suppression Devices:

http://www.apc.com/products/family/index.cfm?id=175

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:34 AM

0 Likes
0
1454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:34 AM

KVar,

You're going to have to narrow that down. There is no isolation or step down transformer within the Symmetra Rack Mount.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:34 AM

0 Likes
0
1456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:34 AM

Kevin,

Is the transformer in that particular UPS a single winding auto-transformer or a dual winding galvanically isolated transformer?

KVAr

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:34 AM

0 Likes
0
1456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:34 AM

It would be bundled with a 120V step-down transformer. The manual shows this model: http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SYTF2 But it has been discontinued, so it may be this model: http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9626

The product page for the Symmetra is here: http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SYH6K6RMT%2DP1&total_watts=500

I talked to APC, and they assured me that Surge Protection and RFI filtering is not required before or after the UPS. He said because it is a double conversion device, the process eliminates any chance of surges or noise, and it produces a completely new pure sine wave.

Anybody have any comments regarding that?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

0 Likes
0
1455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

I would love to know who you spoke to on our end so that they can receive a verbal lashing and maybe some better training. What if the UPS goes to bypass? If you have no EMI/RFI filtering or surge suppression due to a double-online UPS, and it goes to bypass, then that surge is going through the UPS straight to your equipment. Panel Mount Surge is still a great idea to even eliminate a point of entry surge to other devices.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

0 Likes
0
1455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

We are buying it through Dell, and apparently they have a direct number to sales technicians at APC or something. So a Dell rep called me, and then conferenced someone in from APC.

He did not warn me about bypass.

I asked him straight out if I needed to worry about surge supression on the protected side of the UPS and he said no.

But I guess you are right. But under what conditions will automatic bypass occur?

Thanks. Might be worth while investing in some Surge Arresters instead of standard PDUs.

As to the Panel Mount, we are budget constrained. That Sub-Panel strictly serves 2 other Line interactive UPSs. So we should be okay without Panel Mount protection.

Message was edited by: cwatkins

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

0 Likes
0
1456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

Cody,

Automatic bypass will occur any time there is a major fault, and the number of them to list is beyond what I can recall right now. I know for one, a common occurance is "overload bypass" where a power module fails, forcing your load % above 100% (unless you have an added Power Module for redundancy), and forcing it into bypass.

Regarding the surge arrests. You can't look at those since those are just pass throughs, not distributors. Therefore, you won't be able to monitor current flow, and can't ensure that device #5 on the surge arrest is receiving the same amount of power as device #1.

Unless the commercial building is in an area where surges take place quite frequently, you should be all set. Rarely do we ever experience calls regarding any type of damage sustained by a Symmetra to anyone's load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

0 Likes
0
1456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

When you say we "are all set" what to you mean? We do not need to worry about surge protection for the Symmetra? Or we should use a surge arrest or power bar?

Thanks.

Edit: Should mention that no, we are not in an area where we get frequent surges.

Message was edited by: cwatkins

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

0 Likes
0
1455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

There is minimal surge suppression located within the Symmetra, enough that if you're in a low-problem area, it should be able to harness it. When you speak of a Surge-Arrest, the only Surge Arrests that APC sells are single phase 120V surge protectors. What I am speaking of is a Panelmount Surge.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

0 Likes
0
1455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:07 AM . Last Modified: ‎2024-03-08 01:33 AM

Commercial Surge Suppression Devices:

http://www.apc.com/products/family/index.cfm?id=175

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore