I have had a SU3000RMXL3U UPS and a SU48R3XLBP battery pack for about two years now. I wanted to add some time to the setup so I ordered what looked to be the same battery pack, but instead it was a SUA48RMXLBP3U. Is there some way I can make the SUA48RMXLBP3U work with my SU3000RMXL3U? The plug on the new battery pack will not reach and is only half the size as the opening in the older battery pack.
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:30 PM . Last Modified: 2024-03-14 04:26 AM
The SUA48RMXLBP3U supports the following UPSs:
SUA2200RMXL3U
SUA3000RMXL3U
SUA2200R3XLNETPKG
SUA3000R3XLNETPKG
I hope that this helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:30 PM . Last Modified: 2024-03-14 04:26 AM
Carl,
As far as I know, there is no way available to make the SUA48RMXLBP3U work with the SU3000RMXL3U UPS unfortunately.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:30 PM . Last Modified: 2024-03-14 04:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:30 PM . Last Modified: 2024-03-14 04:26 AM
So what ups does it work with. I can't send this battery pack back. It weighs like 200 lbs.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:30 PM . Last Modified: 2024-03-14 04:26 AM
The SUA48RMXLBP3U supports the following UPSs:
SUA2200RMXL3U
SUA3000RMXL3U
SUA2200R3XLNETPKG
SUA3000R3XLNETPKG
I hope that this helps.