Does the Symmetra LX charge batteries while in Maintenance Bypass or even Control Panel Bypass?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Does the Symmetra LX charge batteries while in Maintenance Bypass or even Control Panel Bypass?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

0 Likes
1
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

Does the Symmetra LX charge batteries while in Maintenance Bypass or even Control Panel Bypass?

We had a recent power interruption event and our APC Symmetra was unable to service our Data Centre's need for backup power during the minor black-out (mere seconds). When troubleshooting the issue, we learned that the device was reporting battery faults in the remaining pool of 7 batteries still in the unit. Two batteries of the original nine had been removed in previous weeks due to overheating battery alerts. Unfortunately, we learned during this post power interruption troubleshooting that the UPS was in automated bypass, hence why interruption to the power feed didn't engage the battery system. Battery capacity was listed as 0% and both the soft Bypass was on and Provide Output Power was off. Changing these Control Panel switches restored power to our Data Centre to get our servers back up and running.

Note, both the Symmetra LX and its batteries are now 3 years old.

Now we are in battery replacement mode as well as post event troubleshooting and knowledge acquisition. Under advise by Tech Support, we placed the Maintenance Bypass into the On position (engaging Maintenance Bypass), and removed all of the remaining 6 batteries, and inserted a single new battery. After a few moments, the unit was able to indicate that the battery capacity was at about 25%, and then later in the day installed another new battery (these new batteries arrived in different courier shipments during the business day), now showed battery capacity at 43%. We left the unit in Maintenance Bypass overnight to see if the batteries would charge.

The next day we are showing 23% capacity in the two new batteries. What's going on?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery_charge
  • maintenance_bypass
  • symmetra_lx
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

0 Likes
0
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

Thanks, that explained the problem and the symptoms we saw.

We couldn't get enough Runtime Remaining with the two new batteries, because it was no longer charging the batteries (the two installed power modules were showing Off & OK), so we were forced to install one of the former 6 pulled batteries (none of these 6 had a heat problem) at a time, allowing for the unit to recognize the battery and calculate new Runtime Remaining values. Once all six were in again, together with the two new ones, we noted a Runtime value of 1hr 5min. We felt it would be then safe to come off of Maintenance Bypass to allow the Self-test to run, and Power modules to come back online.

This appeared to work, and the Power modules came back online (On & OK), and all 8 batteries report OK status, but the Self-Test has been running for 1hr 50min, and according to the Overview readings on UPS Network Management session, we are declining now to only 33 minutes of Runtime and Battery Capacity has dropped to 20%. Thirty minutes ago those were 47 minutes of Runtime and 28% Battery Capacity.

Why would the Self-Test take so long? In past months it ran for only a minute or so.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

0 Likes
0
822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

Thanks, that explained the problem and the symptoms we saw.

We couldn't get enough Runtime Remaining with the two new batteries, because it was no longer charging the batteries (the two installed power modules were showing Off & OK), so we were forced to install one of the former 6 pulled batteries (none of these 6 had a heat problem) at a time, allowing for the unit to recognize the battery and calculate new Runtime Remaining values. Once all six were in again, together with the two new ones, we noted a Runtime value of 1hr 5min. We felt it would be then safe to come off of Maintenance Bypass to allow the Self-test to run, and Power modules to come back online.

This appeared to work, and the Power modules came back online (On & OK), and all 8 batteries report OK status, but the Self-Test has been running for 1hr 50min, and according to the Overview readings on UPS Network Management session, we are declining now to only 33 minutes of Runtime and Battery Capacity has dropped to 20%. Thirty minutes ago those were 47 minutes of Runtime and 28% Battery Capacity.

Why would the Self-Test take so long? In past months it ran for only a minute or so.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of