Does PowerChute support Shall / PowerShall command via USB connection?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Does PowerChute support Shall / PowerShall command via USB connection?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

0 Likes
5
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

Does PowerChute support Shall / PowerShall command via USB connection?

Hi all,

I would like to use PowerChute to run Shall / PowerShall command to shutdown ESXi server once power outage, but I have some questions...

 

1. ESXi server connect with UPS via USB connection, is it work?

2. What PowerChute version should I install?

3.How to install?

4.Any alternative methods?

 

Thanks,

 

Stanley 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • PowerChute
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

Hi,

The cable number is 940-0024. Here is a link the the product web page

http://www.apc.com/shop/us/en/products/UPS-Communications-Cable-Smart-Signalling/P-940-0024

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

Hi,

On 4/14/2016 2:27 AM, Stanley said:

1. ESXi server connect with UPS via USB connection, is it work?

No. PowerChute does not support communications to ESXi host via USB. Serial communication is supported. 

On 4/14/2016 2:27 AM, Stanley said:

2. What PowerChute version should I install?

PowerChute Business Edition can be installed on VMware VMA that is running on the ESXi host and configured to power down the host. The scripts to power down the ESXi host are incorporated into PowerChute so there is no need for you to write your own scripts. 

NOTE: PowerChute Business Edition must be connected to a Smart-UPS via Serial comm. 

On 4/14/2016 2:27 AM, Stanley said:

3.How to install?

Please review Knowledge Base documents FA166093 and FA165747 

On 4/14/2016 2:27 AM, Stanley said:

4.Any alternative methods?

You can purchase a Network Management Card for the Smart-UPS and in stall PowerChute Network Shutdown. I also understand that APCUPSD will shutdown ESXi. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

Hi Bill,

 

Thank you for your reply, so you mean PowerChute Business version support USB connection with ESXi server to shutdown once power outage?

 

Thanks,

Stanley

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

0 Likes
0
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

Hi,

No. PowerChute Business Edition does not support USB comm to VMware ESXi host. It does support Serial comm. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

0 Likes
0
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

Hi Bill,

Thank you for your reply, could you mind to tell me this Serial cable is bundle with UPS device package?  Is it LAN to Serial cable?

I am using HPE ProLiant DL380 Gen9 Server with SUA 1500RMI 2U.

 

Thanks,

Stanley

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

0 Likes
0
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:31 AM . Last Modified: ‎2024-03-13 04:14 AM

Hi,

The cable number is 940-0024. Here is a link the the product web page

http://www.apc.com/shop/us/en/products/UPS-Communications-Cable-Smart-Signalling/P-940-0024

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore