Device IP Configuration Utility does not find NMC when SNMPv1 doesn't have public community name

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Device IP Configuration Utility does not find NMC when SNMPv1 doesn't have public community name
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 02:04 AM . Last Modified: ‎2024-03-11 12:16 AM

0 Likes
8
2804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:04 AM . Last Modified: ‎2024-03-11 12:16 AM

Device IP Configuration Utility does not find NMC when SNMPv1 doesn't have public community name

I have been baffled trying to figure out why Device IP Configuration Utility stopped finding devices on the network.  I figured it was a routing change on the network.  Today, the Device IP Configuration Utility did find a device, so I compared the NMC configuration to a device which wasn't found.  I found the NMC which was found had a SNMPv1 community of public, and the device which wasn't found did not have public community.

Reading the help, readme file I didn't see where it needs a public community to work.  Perhaps this could be added to the readme file.  Another option is to allow the user to specify the community which Device IP Configuration Utility uses to search for NMC's.  

I think the public community was removed from the NMC's due to security concerns.

Jeff

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
2804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

Angela,

Thanks for listening and requesting an update to the software!

Jeff

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:04 AM . Last Modified: ‎2024-03-11 12:16 AM

0 Likes
0
2804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:04 AM . Last Modified: ‎2024-03-11 12:16 AM

Hi Jeff,

I will log a product change request about this. You're right that the utility does rely on SNMPv1 and I think the assumption is that the user is finding NMCs on the network for first setup using this tool - which we ship the NMC with SNMPv1 enabled with the default community string of public. Then, of course the user would find the NMC, assign IP settings, and configure it from there, likely never using the utility again after that.

Can I ask more about how you're using this? Are you finding NMCs on the network after first setup for a different reason? Just asking so I can help better explain your perspective and use case in my request so that we are all on the same page.

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 02:04 AM . Last Modified: ‎2024-03-11 12:16 AM

0 Likes
0
2804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:04 AM . Last Modified: ‎2024-03-11 12:16 AM

I would like to know if Device IP Configuration Utility can utilize SNMPv3, so SNMPv1 can be disabled.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:04 AM . Last Modified: ‎2024-03-11 12:16 AM

0 Likes
0
2804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:04 AM . Last Modified: ‎2024-03-11 12:16 AM

Unfortunately no, there is no SNMPv3 support in the utility.

The utility is just designed to find NMCs for first time setup. We don't ship the cards with SNMPv3 enabled by default, especially since SNMPv3 requires some configuration to get it working properly.

I would love to hear more about you're application and how you're using this tool though.

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 02:04 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
2803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:04 AM . Last Modified: ‎2024-03-11 12:15 AM

Angela,

Sometimes I configure a UPS/NMC while it's on my desk, then someone takes the UPS/NMC to a different site (with a different subnet) and they don't assign a DHCP reservation or let me know what IP the NMC picked up.  When the aforementioned happens, I run the Device IP Configuration Utility to find the NMC IP.  I try to prevent this by requesting a DHCP reservation for the remote site ahead of time, however I have been know to make a mistake and forget to request a reservation ahead of time.  Sometimes I remember to check my e-mail to see if I received a startup e-mail from the NMC.  

I also have been know to run Device IP Configuration Utility when I want to ensure all NMC's are on the network--I compare the found list to my list of UPS's.  Ideally I would check my e-mail to see if I had received a self test notification from each NMC, however that's a bit of work.

Thanks,

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:04 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
2803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:04 AM . Last Modified: ‎2024-03-11 12:15 AM

Hi Jeff,

OK, thanks for the background on this. As I said, I'll enter a product change request for the NMC group to review and consideration.

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
2803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

Angela,

I also use Device Up Configuration Utility as a check after upgrading a number of NMC firmwares to determine if I recorded all the upgrades.

 Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
2802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

OK, understood. While I personally understand why you're using this utility and that it can provide a little shortcut for certain tasks, like checking firmware revs, I have a feeling some may argue that it is not the main intent of the utility - especially specific to the firmware rev checking.

The other use case I think is valid and makes sense (again - personal opinion) and I think it will become more important as laws like those being passed in California with non default credentials at least make a case for evaluating the ability to specify a non-default community name for scanning.

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

0 Likes
0
2805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:05 AM . Last Modified: ‎2024-03-11 12:15 AM

Angela,

Thanks for listening and requesting an update to the software!

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore