[Design question] Shutting down vmware vm's and hosts. Smart-UPS SRT 6000 + NMC2

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • [Design question] Shutting down vmware vm's and hosts. Smart-UPS SRT 6000 + NMC2
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:19 PM

0 Likes
7
1848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:19 PM

[Design question] Shutting down vmware vm's and hosts. Smart-UPS SRT 6000 + NMC2

Hello,

What are best practices for a proper shutdown of :

-Windows/Linux virtual machines

-a few ESXi host's, all part of a vmware HA/DRS cluster

Knowing that :

-we have one APC Smart-UPS SRT 6000 with a Network Management Card2.

-we don't want to install powerchute agents on virtual machine's, which would be very unflexible

In the past, I did that with VMware vma appliance and installing PCNS linux package. It was tricky/difficult to maintain since requiring quite advanced scripting skills. Some people in the team weren't comfortable with that.

Now, APC is providing the powerchute network shutdown 3.1 vmware appliance. I deployed and configured that one, but somehow I'm not quite sure it is the right option regarding my hardware component's. So first, if someone could confirm/infirm that point : is it my best option ?

Anyways, I did a shutdown test with the PCNS vmware appliance (while configuring only 1 esxi host being protected) : in my vcenter I get logs saying "unable to shutdown guest operating system in the current state" (vmware tools properly installed/running).  Right after, the VM get's migrated to another host, which is logic considering DRS 🙂

Maybe, do I HAVE to shutdown all ESXi within the same cluster ? I did the previous just in order to test things

Besides of that, I also want to run a script which is stored within my PCNS appliance (under /home)

That script is set with +x rights, and that the path I entered near "Full path to command file" : /home/shutdown.sh

That one does not run at all ? When is it triggered ? after the virtual machines are off maybe or in parallel ?

Thanks for the help

Andreas

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:16 PM . Last Modified: ‎2024-03-14 11:17 PM

0 Likes
0
1848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:16 PM . Last Modified: ‎2024-03-14 11:17 PM

Ok thanks for your help 🙂

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:19 PM

0 Likes
0
1848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:19 PM

for the first part, I started over while adding 2 of my esxi host's into a dedicated cluster for testing : it works, everything (esx hosts/vm's) is shutting down now.

now, the script, "Full path to command file" : /home/shutdown.sh 

still refuses to work, how can I make sure it's even being executed ?

for testing it's launching a simple ping :

#!bin/sh

ping 127.0.0.1 > /home/pingtest -c 5

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:19 PM

0 Likes
0
1848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:19 PM

Hi,

There are 2 issues with your script. First, you need to add / in front of bin example #!/bin/sh Once you do that the script will run and create pingtest in /home however the text file will be blank. If you want to output the results of ping to the text file change line 2 to ping 127.0.0.1 -c 5 | cat > /home/pingtest

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:16 PM . Last Modified: ‎2024-03-14 11:19 PM

0 Likes
0
1848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:16 PM . Last Modified: ‎2024-03-14 11:19 PM

Hi

Happy new year 🙂

Thanks Bill, the #!/bin/sh was the missing part, now the script is running.

Something else :

I browsed across all different menus in the NMC2 as well as in the web interface of the network shutdown appliance, I'm unable to find what I search for.

To be clear : the customer wants the shutdown sequence to be started on one single condition : if the UPS is on battery for >=300 seconds.

Meaning that if the power comes back after 290 seconds the shutdown sequence will not be started and/or immediately aborded

That means we absolutely don't want to react on remaining battery time, which anyways make no sense for me as the remaining battery time is depending on various parameters like the power drained by the equipment which may greatly vary and also depending on the age of the batteries. Very logically, if you plan a shutdown sequence which requiring a definite amount of time but, in the meantime, the available battery time will never be the very same, the whole thing turns in a total non-sense 🙂

Thanks in advance for your suggestions 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:16 PM . Last Modified: ‎2024-03-14 11:18 PM

0 Likes
0
1848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:16 PM . Last Modified: ‎2024-03-14 11:18 PM

Hi,

Log into PCNS and click on Configure Events. You will see a On Battery event. Click on Shutdown - the Enable Shutdown - and enter 300 seconds, click apply.

After the UPS has been on battery for 300 seconds it will start the shutdown process.

7kPH01LM64rGjjcaRRdToQ%3D%3D.png7kPH01LM64rGjjcaRRdToQ%3D%3D.png

0OmAYuDrsCLgAXh3LGHf3g%3D%3D.png0OmAYuDrsCLgAXh3LGHf3g%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:16 PM . Last Modified: ‎2024-03-14 11:18 PM

0 Likes
0
1848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:16 PM . Last Modified: ‎2024-03-14 11:18 PM

Thanks ! And if the power is back after 250seconds it gets canceled, right ?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:16 PM . Last Modified: ‎2024-03-14 11:18 PM

0 Likes
0
1848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:16 PM . Last Modified: ‎2024-03-14 11:18 PM

Hi,

It does not get cancelled because it does not start the shutdown process until the UPS has been on battery for 300 seconds.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:16 PM . Last Modified: ‎2024-03-14 11:17 PM

0 Likes
0
1849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:16 PM . Last Modified: ‎2024-03-14 11:17 PM

Ok thanks for your help 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of