Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

BackupUPS RS 1500 on Windows Server 2003

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • BackupUPS RS 1500 on Windows Server 2003
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:20 PM

0 Likes
3
1514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:20 PM

BackupUPS RS 1500 on Windows Server 2003

I used APC's website to recommend a trade-in for a SU1400 on a Windows Server. They recommended the BackupUPS RS 1500. Now I find it only works with PowerChute Personal Edition which won't run on a server OS. What gives??

I downloaded and installed PowerChute Business Edition 8.01, which recognized the Back UPS 1500 during installation, but now that it's installed I see "Device Communications Not Established".

There are many features of Business Edition which I would love to have, but more than anything I would like this UPS to work!!! I only need the software to be able to shutdown the computer safely in the event of an extended power outage, and I only need to manage this one UPS on this one Windows SBS 2003 Server.

Any suggestions??? Thanks for your help!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • backup_ups_rs_1500
  • powerchute_business_edition_8.01
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:20 PM

0 Likes
0
1514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:20 PM

Andrew,

You may want to contact Microsoft for help but be aware they have announced end of support for Windows Server 2003 beginning 14 July 2015. If native does not / is not work you can look at APCUPSD. It supports Windows Server 2003 including 64 bit, has a binary /.exe installer, and support comm Over USB.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:20 PM

0 Likes
0
1514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:20 PM

Shannon,

The Back UPS RS 1500 is a simple signaling UPS, where as the Smart UPS uses Smart Signaling for the advanced monitoring purpose. The Power Chute Business Edition will not communicate with the Back UPS through the USB cable.

The PCBE will have limited options even if it communicates with it via the appropriate cable because it is the simple signaling UPS. You may configure the USB native support to shutdown your Server gracefully in the event of power failure. You would need to uninstall the Power Chute software in order for the Windows USB native support to enable.

Please make use of the below K-base document instructions to configure the USB native support after uninstalling the Power Chute software from your server.
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2497

I hope that it helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:20 PM

0 Likes
0
1514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:20 PM

Looking for a way to configure the native UPS support in Windows 2003 Server but am having problems with the slider bars for low and critical battery level alarms.  They always jump to 100%, regardless of what I try to set them to.

UPS is Back-UPS XS 1300

Also, the low battery alarm triggers immediately that the UPS goes onto battery - which makes the UPS controls simply useless.

Anyone able to suggest how to:

a)   configure Windows 2003 server to have realistic low and critical battery alarm levels?

b)   use APC software to allow UPS to be used properly.

BTW - the link in the thread above does not work.

Thanks,

A

  • Tags:
  • 2003
  • server
  • windows
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:20 PM

0 Likes
0
1515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 PM . Last Modified: ‎2024-03-14 11:20 PM

Andrew,

You may want to contact Microsoft for help but be aware they have announced end of support for Windows Server 2003 beginning 14 July 2015. If native does not / is not work you can look at APCUPSD. It supports Windows Server 2003 including 64 bit, has a binary /.exe installer, and support comm Over USB.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore