I can't figure out why ours ACRD101 units are not dehumidifying. Temperature is kept correctly, while humidity reaches over 70% during summer (today is round 40%) according to NetBotz.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:29 AM . Last Modified: 2024-01-31 03:04 AM
Thank you for clarification.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:29 AM . Last Modified: 2024-01-31 03:04 AM
Hello Zeljko. The ACRD101 does not have de humidification. It is just a straight cooling unit. The unit will dehumidify a little while it cooling but it does not have the capability to straight dehumidify. Only the ACRP101 or the ACRD601P will have the de humidification capability.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:29 AM . Last Modified: 2024-01-31 03:04 AM
Thank you for clarification.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.