ACRD602P Low Suction Pressure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ACRD602P Low Suction Pressure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:26 AM . Last Modified: ‎2024-02-14 10:21 PM

0 Likes
18
8891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:26 AM . Last Modified: ‎2024-02-14 10:21 PM

ACRD602P Low Suction Pressure

Hello dears,

I have three units of ACRD602P working as HACS, the three units located in one Datacenter.

Before 29 OCT the units were working as InRow, one of the units (CB1) gives Low Suction Pressure at 10:00 AM, and all the cooling system stopped working, the DC temp become very high.

First Question, why if one unit has a fault, the others unit become not working?

2- Why the unit gives Low Suction Pressure?

All the two units charged by 32kG and the third 33kG of Gas due to these calculations:

5.5kg+7.7kg+12.4kg+(18.6*0.28)kg=30.8kg + 2valve =32.8kg

For unit 3 about

 5.5+7.7+12.4 +(20.93*0.28)= 31.46kg + 2valve=33.46kg

The Supply Air temperature before install the flood receiver was 15c, now and after the flood receiver installing and charge the unit with 20kG gas in addition to the 10kG existed, the supply air temperature become 14c and some times 13c.

What is nominal supply air temperature?

What is the main function of the flood receiver?

What is the minimum suction pressure for the unit?

What is the nominal suction pressure for the unit?

What is the nominal discharge pressure for the unit?

What is the nominal suction temperature?

Attachments
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:28 AM . Last Modified: ‎2024-02-14 10:20 PM

0 Likes
0
8889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:28 AM . Last Modified: ‎2024-02-14 10:20 PM

Ok, i will upgrade firmware.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 18
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

0 Likes
0
8889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

Hello Rami. The normal suction pressure for R410A is between 120 and 140psi and the discharge pressure is between 250 and 270psi. The unit will go off on low suction once the suction pressure reaches about 90psi. There are many reasons that this unit could have gone off on low suction. There could be a leak somewhere. It could be a low load issue. Do you have the load on this unit? As to why the other unit did not come on, there are a few variables to this. Are the units in a group and linked together or are they separate? What mode (type) are the units set to? Are the units all set to "On" or are the units in "Standby"? For the receiver, this is to store extra refrigerant. This is needed as the temperature changes throughout the year, the amount of refrigerant needed changes. In the winter, the refrigerant will pool in the condenser as it is the coldest place in the circuit. The extra refrigerant in the system will be needed to keep the pressures in the system up for the unit to operate. In the summer the extra refrigerant is stored in the receiver. 

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

0 Likes
0
8889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

Hello Sir,

Thank you for your information

I don't think that we have leak in the units, because the unit is working Ok for a long, but sometimes it give this alarm.

The Datacenter load is very low, because of that I made the new configuration to HACS and turn on unit on and make the rest two units in Backup mode.

Are the units in a group and linked together or are they separate? 

Yes they are connected via A-Link and we have two Units of AFC

the units connected like this: Terminator - AC1-AC3-AFC-AC2-AFC-Terminator.

What mode (type) are the units set to? 

They was InRow, I made them recently HACS (because Ihave hot aisle)

 Are the units all set to "On" or are the units in "Standby"? 

All Were On

what do you suggest to test the Gas quantity in the units?

How can I log the Suction pressure on the units?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

0 Likes
0
8889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

Hello Rami. The best things to do form here is first check the sight glass to see if there are any bubbles in the refrigerant that would indicate a low charge. Also pull the data logs off the network card (they can be found under the web interface under logs-data-log.) This records the suction pressure for the unit along with other values. You can set the interval from 10 min down to 1 min if it is not catching the low suction pressures. Also check the load values on the data log. We would like to see at least 15kw load on the unit. If it is getting below this, the low load could be causing the low suction. As you have a HACS system, make sure there are no open spaces in the racks or in the rows to help increase the load.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

0 Likes
0
8889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

Dear Sir,

I'm attaching the Events and Datalogs, I will also take them out tomorrow and back to you

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

Hello,

I'm attaching updated log files

by the way, the unit didn't gives low suction press alarm in the days when the log recorded 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

Hello Rami. From the logs provided, I would put this on the low load in the room. The unit 1 is running for 30  to 40 min then shutting down as it has satisfied its cooling demand. It will then sit off between a half to one and a half hours. Are there plans to add more load to the room? When the units are off the refrigerant will migrate to the coldest place in the system. This is usually the condenser outside. When the unit starts back up it will sometimes take a couple of tries to get the refrigerant moving through the entire system again. More heat load will keep the system on longer and keep the refrigerant from migrating to the condenser.  we can try putting the units back to inrow mode until more heat load is added if they were working before changing it to HACS.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

Dear Sir,

The customer is planning to install extra equipments the Datacenter, I tried to make the units to be InRow, but the three units will be ON, and not one On and Two backup, what do you suggest to make them in the write configuration?

Also I found that the supply air humidity is more than 82%, what I should do?

what are the best parameters and set point for my case?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

Dear Sir,

The customer is planning to install extra equipments the Datacenter, I tried to make the units to be InRow, but the three units will be ON, and not one On and Two backup, what do you suggest to make them in the write configuration?

Also I found that the supply air humidity is more than 82%, what I should do?

what are the best parameters and set point for my case?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:21 PM

Dear Sir, I'm waiting for your kind reply

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:20 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:20 PM

Hello Rami. The return humidity is showing between 58% and 75% for the units. This is pretty high for room humid. The supply humid will read higher as relative humidity is dependant on the temperature. As we are outputting cooler air on the supply side, the relative humidity will go up. The cooling units will dehumidify a little while cooling but are not able to keep the entire room humidity down. To help out the humidity levels, you can raise the supply air temperature setpoint and make sure the reheat is enabled on the cooling units. This will help a bit but if there is humidity coming in from the outside, the only way to get the humid down would be to either seal the room or supplemental de humidification.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:20 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:20 PM

Dear Sir,

There are no out humidity, I will increase the supply set point to 24C, by the way it is now 23C

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:20 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:20 PM

Dear Sir,

Please check the attached Datalog 

The Supply humidity is 100% in CB3, CB1 and CB2 are Backup units.

I have made the supply air set point to 24C, and the coolant set point to 25C

By the way, I found water in CB3 radiator

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:20 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:27 AM . Last Modified: ‎2024-02-14 10:20 PM

Hello. When the unit does turn on to cool, it is cooling very fast and the supply air is getting lower then the dewpoint is is causing the supply humid reading to spike to 100%. To assist this unit in the low load situation, is the reheat enabled? Also what is the setpoint for the reheat? Try setting the reheat to 18 or 19C.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:28 AM . Last Modified: ‎2024-02-14 10:20 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:28 AM . Last Modified: ‎2024-02-14 10:20 PM

Dear Sir,

The Reheat and Heat assistant are enabled, The reheat is 14C, I will make it to 19C due to your recommendation.

By the way, today I got new warning from one of the units, it is Low Superheat warning 

Please check:

11/13/2017 13:15:43 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 13:15:34 Device Low Superheat Warning. 0x40BA
11/13/2017 12:55:42 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 12:55:34 Device Low Superheat Warning. 0x40BA
11/13/2017 12:35:59 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 12:35:50 Device Low Superheat Warning. 0x40BA
11/13/2017 12:15:50 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 12:15:41 Device Low Superheat Warning. 0x40BA
11/13/2017 11:36:23 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 11:36:15 Device Low Superheat Warning. 0x40BA
11/13/2017 11:16:31 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 11:16:23 Device Low Superheat Warning. 0x40BA
11/13/2017 10:56:48 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 10:56:39 Device Low Superheat Warning. 0x40BA
11/13/2017 10:37:22 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 10:37:14 Device Low Superheat Warning. 0x40BA
11/13/2017 10:18:05 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 10:17:56 Device Low Superheat Warning. 0x40BA
11/13/2017 09:58:05 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 09:57:56 Device Low Superheat Warning. 0x40BA
11/13/2017 09:19:22 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 09:19:13 Device Low Superheat Warning. 0x40BA
11/13/2017 08:59:30 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 08:59:21 Device Low Superheat Warning. 0x40BA
11/13/2017 08:20:12 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 08:20:03 Device Low Superheat Warning. 0x40BA
11/13/2017 07:41:12 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 07:41:03 Device Low Superheat Warning. 0x40BA
11/13/2017 05:44:37 Device Low Superheat Warning Cleared. 0x40B9
11/13/2017 05:44:28 Device Low Superheat Warning. 0x40BA
I tried to understand the problem, I found that at the times which the unit give the low superheat warning, the superheat become lower than -16.6C, and the Output load is going to Zero!
I summarized the datalog for you, please check it
I make the time with problem occur in red  
Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:28 AM . Last Modified: ‎2024-02-14 10:20 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:28 AM . Last Modified: ‎2024-02-14 10:20 PM

Hello. What is the firmware version on the web interface for this unit? There should be an aos and app version.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:28 AM . Last Modified: ‎2024-02-14 10:20 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:28 AM . Last Modified: ‎2024-02-14 10:20 PM

firmware version on the web interface of this unit:

Factory Information
Hardware Factory
Model Number
0N-9580AC
Serial Number
JK1712002547
Hardware Revision
06
Manufacture Date
03/30/2017
MAC Address
00 C0 B7 F5 F6 26
Management Uptime
0 Days 4 Hours 41 Minutes
Network Management Card
Serial Number
JD1713001244
Application Module
Name
acrd2g
Version
v6.3.3.g
Date
Apr 13 2016
Time
11:23:18
APC OS (AOS)
Name
aos
Version
v6.4.0
Date
Dec 18 2015
Time
15:10:21
APC Boot Monitor
Name
bootmon
Version
v1.0.8
Date
Apr 8 2014
Time
11:00:33
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:28 AM . Last Modified: ‎2024-02-14 10:20 PM

0 Likes
0
8888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:28 AM . Last Modified: ‎2024-02-14 10:20 PM

Mahmoud,

Please try upgrading to the latest firmware version, AOS 6.4.4/ACRD2G 6.3.4

I have attached it for you.

Thank you.

Attachments
apc_hw06_aos644_acrd2g634_bootmon108.zip
apc_hw06_aos640_acrd2g633_bootmon108.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:28 AM . Last Modified: ‎2024-02-14 10:20 PM

0 Likes
0
8890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:28 AM . Last Modified: ‎2024-02-14 10:20 PM

Ok, i will upgrade firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of