Deciding between Smart UPS & Backup Pro

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Deciding between Smart UPS & Backup Pro
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

0 Likes
6
6756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

Deciding between Smart UPS & Backup Pro

I'm trying to decide between the Smart UPS & Backup Pro line. I know that the Backup Pro line is more for home PC's and that the Smart UPS line is more for business networks. I currently have a laptop, desktop, oversized monitor, cable modem, router, NAS and printer at this point, but addtional components could be added in the future.

I noticed that the Smart UPS line offers a pure sine wave where as the Backup Pro line does not. How important is this?

I looked at the projected runtime for the Backup Pro 1000 vs. the Smart UPS 1000 under a 600W load and there's not that much of a difference. However, there is a notable difference between the 1500 models.

It also looks like there are more "battery backup" outlets on the Smart UPS vs. the Backup Pro. Half of the outlets on the Backup Pro are for surge protection only.

I like the option for the network management card on the Smart UPS, but I probably will never use it.

I am really looking for a quality UPS that will provide about 10 minutes of up time, support for gracefully powering down my systems, power conditioning and ample sureg protection.

What do you think? Smart UPS or Backup Pro?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

0 Likes
0
6747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

Hi,
having used stepped approximation units for many years, I recently had to switch to sinewave units.

First reason is that newer power supplies have PFC or A-PFC, and that does not bode well with stepped output.

Also, the crest factor of the stepped is not as high as sinewave outputs (for APC that is).

The third reason is that higher power stepped units do put out a peak to peak voltage which is dangerously close to the maximum voltage rating of capacitors inside the attached power supplies.

There are a few more reasons,these are the main only.

However, as long as you only have the mentioned parts, and they are not newer than 1 year, you could still use stepped units.

But to be totally save and compatible with future high efficiency power supplies, I'd recommend sine.

And the runtime is ONLY dependent on the batteries used, the efficiency of stepped/sine is nearly the same.

So whoever uses larger Ah batteries, runs longer.

P

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

0 Likes
0
6747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

Bump.

Can anybody help me with this?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

0 Likes
0
6747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

Honestly, I'd just go for the backups unit. I don't honestly think you need the features of the smartups. For example, you don't need a pricey network management card if you've got only two computers, one of which has a built-in ups to begin with. And you don't need too many ups ports; you only REALLY need one to keep the computer powered while it shuts down. Your network gear will be fine without ups power; according to your post your intent is not to keep the network/ISP link up and running as long as possible anyway.

I'm a total nerd that spends too much time and money on home computer/network gear, so I happen to use smartups units even though my needs are similar. I'd say that these are for people who either know they need it or know they want the fancy features. You don't seem to be in either camp. HTH!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

0 Likes
0
6747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

Are you looking at safely shutting down the desktop PC, if yes what Operating System are they using? I would also check first the load that you are going to connect, would they require a pure sine wave or would they accept a quasi/square/step approximated sine wave? Are you using generator, if you do our Smart-UPS works well with generators.

I would recommend using a Smart-UPS if all of the load needs to have back up power since all of it's outlets are battery backup and surge outlets unlike the BackUPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

0 Likes
0
6747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

Did you read the first post? This is a user with a basic understanding of UPS tech, and a simple set of needs. They're wondering if a basic unit would be sufficient for those needs. The short answer is yes, it would be sufficient.

Are you looking at safely shutting down the desktop PC

They said yes in the first post, but both units offer that functionality.

would they require a pure sine wave or would they accept a quasi/square/step approximated sine wave?

They don't know, which is why they asked to begin with. Given the context of the post, it is almost certain that nothing they have requires a pure waveform.

Are you using generator

Are you serious?

I would recommend using a Smart-UPS if all of the load needs to have back up power since all of it's outlets are battery backup and surge outlets unlike the BackUPS.

The post states that they already know not every outlet on the backups gets UPS power. They're asking for help in determining whether this is significant. I'm saying that it's insignificant in this context because the vast majority of that equipment does NOT need UPS power.

With respect to your reputation medal and what it implies, it seems that in this case you aren't really helping the user even though you're asking the technically correct questions. To reiterate my first response, people who need the functionality of the SmartUPS generally know they need it. If you have to ask, then you're almost certainly not among them. The extra features may be desirable, but that's something no one else can help you with.

Message was edited by: curby

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

0 Likes
0
6747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

I apologize I missed that part that jjscott has posted. Let us move on and assist jjscott with his issues.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

0 Likes
0
6748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:42 AM . Last Modified: ‎2024-03-13 03:21 AM

Hi,
having used stepped approximation units for many years, I recently had to switch to sinewave units.

First reason is that newer power supplies have PFC or A-PFC, and that does not bode well with stepped output.

Also, the crest factor of the stepped is not as high as sinewave outputs (for APC that is).

The third reason is that higher power stepped units do put out a peak to peak voltage which is dangerously close to the maximum voltage rating of capacitors inside the attached power supplies.

There are a few more reasons,these are the main only.

However, as long as you only have the mentioned parts, and they are not newer than 1 year, you could still use stepped units.

But to be totally save and compatible with future high efficiency power supplies, I'd recommend sine.

And the runtime is ONLY dependent on the batteries used, the efficiency of stepped/sine is nearly the same.

So whoever uses larger Ah batteries, runs longer.

P

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore