DIY project: recover AP9631 card with blank mac address, model number etc

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • DIY project: recover AP9631 card with blank mac address, model number etc
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Arek
Arek
Cadet

Posted: ‎2025-08-26 01:59 PM

0 Likes
1
203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-26 01:59 PM

DIY project: recover AP9631 card with blank mac address, model number etc

This is DIY project for fun.

My AP9631 card has blank factory region which means blank mac address, blank model number and so on.

 

This card has Spansion S29JL064J55TFI00 64Mb parallel flash in TSOP48 package. Dumping it with programmer (used XGecu 76 + TSOP56 adapter, which also handles TSOP48 ) reveals that all factory data is in first few bytes. I'm trying to figure out meaning of these. Half guessed/half known information below:

Offs  Len   Raw bytes                                Meaning / notes
----  ---   ---------------------------------------  ------------------------------
0x00  1     01                                       Format major = 1 (?)
0x01  1     00                                       Format minor = 0 (?)
0x02  2     30 35                                    ASCII "05" → revision
0x04  2     00 00                                    Reserved / padding (?)
0x06  13    FF ... FF                                Erased flash padding
0x13  11    30 36 2F 32 34 2F 32 30 31 31            ASCII "06/24/2011" (build date)
0x1E  9     41 50 39 36 33 31 43 48 00               ASCII "AP9631CH" + NUL (model)
0x27  8     FF ... FF                                Padding
0x2F  13    35 41 31 31 32 36 54 31 30 00 00 00 00   ASCII "5A1126T10000" + NUL (serial)
0x3C  20    FF ... FF                                Padding
0x50  6     00 C0 B7 C4 00 00                        MAC address = 00:C0:B7:C4:00:00
0x56  2     00 01                                    Language = 1 (?)
0x58  2     00 01                                    International = 1 (?)
0x5A  1     00                                       Padding / align before checksum
0x5B  4     EF 7B 12 17                              Checksum / CRC (polynomial TBD)
0x5F  1     FF                                       Padding
0x60  4     FF FF FF FF                              Padding

and a lot of FF FF until actual firmware


(note; changed mac address and serial number in above by hand)

Cloning some other card makes my problematic card working but I don't want to do that. I want to restore proper MAC address, model name, serial number (all from stickers). Unfortunately changing only these will cause card to behave just like broken card - no mac, no model number.


The secret most likely hides in checksum. So far was unable to figure out algorithm used for that and create proper checksum for my mac, serial.

Does anyone have an idea how that checksum is calculated?

Also I'm interested in dumps from other AP963x cards, if anyone have a programmer and is able to do that give me a note.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Arek
Arek
Cadet

Posted: ‎2025-08-27 08:06 AM

0 Likes
0
183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-27 08:06 AM

It seems to be CRC-16/CCITT-FALSE. At least that worked for me and boot monitor shows "CRC = OK" now.

Card is fully recovered, has original model name, mac, serial, revision, date. I also was able to update to latest 7.2.0 firmware.

Only "EF 7B" is a checksum. "12 17" meaning is unknown.

https://github.com/arekm/ap9631-recovery

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore