DHCP Configurations No Longer Working

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • DHCP Configurations No Longer Working
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:51 PM

0 Likes
4
818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:51 PM

DHCP Configurations No Longer Working

So we have used X3000 UPS's extensivly for a number of years.  Up until about a year ago we were able to generate aq configuration and apply it via DHCP for every deployment.  This would include user information.  Now with the newer firmware it seems that this has been broken.   The user configuration is now in a seperate file or has to be set manually and I don't see a way for these to be applied via DHCP which kind of negates any automatic configuration.

So does anyone have any best practices on applying the configuration both system and user, via DHCP to make this an automated process again?

Any help is appreciated, thanks!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

Hi Nick,

Yes, the firmware on your UPS itself (7.4) doesn't matter for this NMC issue. I was referring to the firmware on the NMC that you eventually looked at. v6.1.1 is older FYI, AOS/sumx app is v6.2.1 is the latest and available for download @ http://www.apc.com/tools/download/index.cfm. And again, it does not fix this issue but has several other bug fixes in it if you wanted to upgrade.

The v6.3.X will be out later this year as I mentioned and be on our website I suspect around Nov/Dec but that can change.

Yes, it seems to have broken on v6 firmware. v5 and v6 are just completely different platforms under the hood so I have told the QA team to make sure we are actively testing this each release as we should've been anyway.

Lastly, users can/will not be configured through config.ini any longer unfortunately and is by design. Mass configuration of users is now handled via a separate .csf file and how to do it is explained here (and you can use that same INI utility to cascade the file out to NMCs)-> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA176542 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:51 PM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:51 PM

Hi Nick,

Are you referring to the DHCP boot file name option mentioned here -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA156110 ?

If so, yes, it broke (caused the NMC to go into a reboot loop) and someone else posted about it a little bit ago here. I believe it will be fixed in a version of v6.3.X firmware for AP9630/31 coming out later this year as I was the one who logged the bug.

We have other options of automating a push of a config.ini file after DHCP configuration for now as an option but that is about it until the issue gets fixed that I am aware of without using our StruxureWare product. (Information on that here with the utility available -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA156117 )

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

Thanks for the reply.  I can say for sure that it's been broke for me since the X3000's started to come with the Schneider Firmware.  Right now it looks like I am running 7.4 (ID1003). So how can I have newer firmware than the version you just mentioned?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

Never mind I see that my AOS version is 6.1.1.  So with the update to 6.3.x later this year, I will be able to completly configure my UPS again with an INI file?  This would include users as well?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

Hi Nick,

Yes, the firmware on your UPS itself (7.4) doesn't matter for this NMC issue. I was referring to the firmware on the NMC that you eventually looked at. v6.1.1 is older FYI, AOS/sumx app is v6.2.1 is the latest and available for download @ http://www.apc.com/tools/download/index.cfm. And again, it does not fix this issue but has several other bug fixes in it if you wanted to upgrade.

The v6.3.X will be out later this year as I mentioned and be on our website I suspect around Nov/Dec but that can change.

Yes, it seems to have broken on v6 firmware. v5 and v6 are just completely different platforms under the hood so I have told the QA team to make sure we are actively testing this each release as we should've been anyway.

Lastly, users can/will not be configured through config.ini any longer unfortunately and is by design. Mass configuration of users is now handled via a separate .csf file and how to do it is explained here (and you can use that same INI utility to cascade the file out to NMCs)-> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA176542 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of