AP6919 cannot set IP via ARP

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP6919 cannot set IP via ARP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
15
5146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

AP6919 cannot set IP via ARP

I have APC Smart-UPS RT 5000 with AP6919 NMC. I tried to set IP to that NMC via ARP with below step:

First, I see the AP6919 ethernet port led status is flashing green, then I connect my Windows 7 pc directly to AP6919 with one straight cable (p2p). The led status still flashing green and ethernet led is turn on with solid orange color.

Second, in Windows 7 pc, I run "arp -s 192.168.13.100 xx-xx-xx-xx-xx-xx"  as  admin, it done without error. So  I run "ping 192.168.13.100 -l 113" and the result is Request timed out.

Can someone help me with these problem, is there any miss or wrong step I do while setting the NMC? Thank You.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap6919
  • ARP
  • ip
  • NMC
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

You're welcome!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

Here are my thoughts:

  • I assume you set the IP on your PC on the same subnet as the IP you'd like to use on your AP9619? 
  • I would try to press and release the pinhole reset button on the AP9619 once and repeat trying ARP.
  • You could also try running the APC Device IP Config Wizard through this peer to peer direct connection as well if ARP isn't working and see if the wizard finds the management card.

A flashing green status LED means invalid IP settings. It can also happen after DHCP/BOOTP requests timeout, hence me telling you to press and release the pinhole reset button to get it to try DHCP(and BOOTP) again. If the flashing green status LED persists, then there may be mean there is an invalid manual address set on the NMC in which case ARP will not likely work and you may want to establish a serial connection to the AP9619. It would also likely mean that the Device IP Config wizard I mentioned would not work unless you know the IP range the AP9619 may have had to do a search.

Another option if you can't do serial and to see if there is an (invalid) IP present is to do a packet capture/Wireshark via the direct connection and see if you can see the IP of the AP9619 via there.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:09 AM . Last Modified: ‎2024-02-29 10:50 PM

On 8/11/2015 8:27 PM, Angela said:

I assume you set the IP on your PC on the same subnet as the IP you'd like to use on your AP9619? 

Yes, my Windows 7 IP is 192.168.13.253/24.

On 8/11/2015 8:27 PM, Angela said:

I would try to press and release the pinhole reset button on the AP9619 once and repeat trying ARP.

When i press and release the reset button, the led status rapidly flashing green and orange. Should I press the reset button again? Actually, I already tried both and seems like the result is same. Or is there any different between press->release and press->release->press?

On 8/11/2015 8:27 PM, Angela said:

You could also try running the APC Device IP Config Wizard through this peer to peer direct connection as well if ARP isn't working and see if the wizard finds the management card.

I already tried the Device IP Config Wizard before using ARP method. I run scan with the offline tab and no apc device found. Also try the online tab by guessing the ip range, but still not finding any apc device.

On 8/11/2015 8:27 PM, Angela said:

A flashing green status LED means invalid IP settings. It can also happen after DHCP/BOOTP requests timeout, hence me telling you to press and release the pinhole reset button to get it to try DHCP(and BOOTP) again. If the flashing green status LED persists, then there may be mean there is an invalid manual address set on the NMC in which case ARP will not likely work and you may want to establish a serial connection to the AP9619. It would also likely mean that the Device IP Config wizard I mentioned would not work unless you know the IP range the AP9619 may have had to do a search.

In the end, the led status still flashing green and ethernet  led still solid orange (sometime it flashing). By using reset button not reset the IP config? Or serial connection is the only way to reset IP config?

On 8/11/2015 8:27 PM, Angela said:

Another option if you can't do serial and to see if there is an (invalid) IP present is to do a packet capture/Wireshark via the direct connection and see if you can see the IP of the AP9619 via there.

Yup, I don't have the apc serial cable. If its the only way, I'm planning to buy a new cable. Is this correct?

And is it possible the NMC is broken or faulty, how can i check it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

Hi Mytosin,

On 8/12/2015 3:02 AM, Mytosin said:

When i press and release the reset button, the led status rapidly flashing green and orange. Should I press the reset button again? Actually, I already tried both and seems like the result is same. Or is there any different between press->release and press->release->press?

Pressing once and releasing is a soft restart. Pressing once, seeing the lights, and pressing again starts the password reset procedure. The important part is what happens after the LED rapidly flashes green and orange. The rapid green and orange just means its rebooting and should stop after 10-15 seconds.

On 8/12/2015 3:02 AM, Mytosin said:

In the end, the led status still flashing green and ethernet  led still solid orange (sometime it flashing). By using reset button not reset the IP config? Or serial connection is the only way to reset IP config?

Do you ever see anything else after status LED rapidly flashing green and orange but before flashing green? The reset button on this model of NMC only allows soft reboot of the management interface or to do the password reset procedure. On newer models - AP9630/31/35, it does allow a full factory reset without having to log in. On this one, you'll have to gain access via the serial interface or by figuring out what the IP is.

On 8/12/2015 3:02 AM, Mytosin said:

Yup, I don't have the apc serial cable. If its the only way, I'm planning to buy a new cable. Is this correct?

And is it possible the NMC is broken or faulty, how can i check it?

If you know how to make cables, you may be able to find the pinout there on the internet but I can't post it here for you. Otherwise, yes what you linked to is correct, purchase whatever you can find cheapest - either the 6 ft version, part number 940-0024 or 15 foot version - 940-1524. Either one will work.

I don't think it is broken based on the light combination. If I had any concerns based on what you've described that the NMC itself was broken, I'd let you know but I see no evidence. What it sounds like is that this has been configured before or has some invalid IP settings on it, assuming my new questions on the status LED I posted above do not indicate anything different.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

Hi Angela,

On 8/13/2015 12:43 AM, Angela said:

I don't think it is broken based on the light combination. If I had any concerns based on what you've described that the NMC itself was broken, I'd let you know but I see no evidence. What it sounds like is that this has been configured before or has some invalid IP settings on it, assuming my new questions on the status LED I posted above do not indicate anything different.

After the led status stop flashing green and orange, it become orange for 1s then start to flashing green. Is it hardware failure like the manual say?

And if the NMC is broken, can i replace it with new NMC like AP9630?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

The manual says solid orange for the status LED is a hardware fault and it should persist if that were the case, not only show for 1 second. I think it's been configured before and has some invalid settings programmed and needs to be connected to serially. I do not think it is a hardware fault.

If you don't want to work on it further, then yes, AP9630/31 will work with this UPS.

Actually, you said Smart-UPS 5000 RT before - can you check the model/SKU number? Is it SURT5000XLI or SURTD5000XLI. I made a poor assumption there - the serial cable for SURT5000XLI would be 940-0024 or 940-1524 as we discussed. If it is SURTD5000XLI, then it'd have an RJ-45 style serial port and be 940-0625 you'd want to look for (or 940-1525).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

Yes, it's SURT5000XLI with serial port.

The conclusion is we are about to order a new cable and try the serial connection first before decide to buy a new NMC.

Thank you for helping me out and providing the information, I truly appreciate your help in resolving the problem. laughing

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

You're very welcome. Look forward to helping you get it 100% resolved!

Reply

Link copied. Please paste this link to share this article on your social media post.

bbiandov_apc
Lieutenant JG bbiandov_apc
Lieutenant JG

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

Hi Angela,

I know it's an old post but it is only relevant to my issue - which is identical as the one discussed here.

My AP 9619 can't get IP and WireShark is reporting malformed DHCP packet. All I did was change from static IP to DHCP using the GUI web interface. Now the thing would not get an IP; the arp method fails; the Device IP Configuration Utility fails.

Pinhole reset responds as expected meaning the LED sequence makes sense but the NMC can never get IP.

The status LED slowly flashes from amber to green which is consistent with the status of "getting DHCP address". I don't have the serial cable, this is RT 5000-X: unit.

Thank you

~B

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

Hi Boyan,

I understand what you said about the malformed packet but I also don't see how that would occur randomly. I also don't know what firmware is on this older card and if it'd truly prevent the device from getting an IP.

Putting the DHCP malformed packet observation aside, I was wondering if configuring option 43 (DHCP cookie) would help. This is enabled by default and unless you know you specifically disabled it, could be causing the problem. There is some info on it here -> http://www.apc.com/us/en/faqs/FA156110

We have made this disabled by default on newer devices to cause less headache. On your model, we'd have to log in and change it via serial connection which I know you said you don't have the cable. You don't happen to be using this with a UPS that has a display that supports configuring the card, do you? Or can we move it to a different UPS by chance you do have the cable for?

Reply

Link copied. Please paste this link to share this article on your social media post.

bbiandov_apc
Lieutenant JG bbiandov_apc
Lieutenant JG

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

Thanks Angela,

I will test by configuring option 43 on my DHCP. The UPS does not have display and I don't have one with a display - they are all the same RT 5000 - no display. 

I'll report results ASAP from the DHCP option configuration change. Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

OK, another option will be maybe to try using the APC Device IP Configuration Wizard software. You can run it on a PC on the same network as the AP9619 and see if it can pick it up to temporary gain access back into it using a static IP.

That software is here: http://www.apc.com/us/en/tools/download/ and look for Software Upgrades - Wizards and configurations. Then check for the item on the list with part number SFDIPW502. It is a Windows utility and would theoretically work if the AP9619 has firmware 3.X.X.

Reply

Link copied. Please paste this link to share this article on your social media post.

bbiandov_apc
Lieutenant JG bbiandov_apc
Lieutenant JG

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

Thanks Angela,

The IP Configuration Utility v5.0.2 finds the mac address of NMC but fails to set an IP address; I get a java ARP error and then another java looking window that says the device already has an IP address assigned to it?

I will still do the DHCP option test but also I was looking to prepare for possible next steps: is there a way to "factory reset" those NMC v1 cards meaning either remotely re-load the firmware via some tftp boot strap method or physically remove the NMC from the UPS unit and do some factory reset on the board; a DIP switch; jtag method; something like that?

Thanks

~B

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

Hmm. I would make sure also to run the utility as an administrator to rule out any permissions problems with the background commands. 

With this model of card unfortunately, there is no way to reset this remotely or without logging in. No dip switches. The newer AP9630/31/35 devices or anything using a mini version of it allows you to hold down the reset button to do a "format" or factory reset. This is not available on AP9619 unfortunately.

Only option will be to access it via serially on your current UPS or a different UPS or something cry

Reply

Link copied. Please paste this link to share this article on your social media post.

bbiandov_apc
Lieutenant JG bbiandov_apc
Lieutenant JG

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

Hi Angla,

It was the cookie! I happened to find the serial cable and I was able to confirm and then reverse it. Then DHCP worked right away.

Thank you

Boyan

ekEw6YafVizv5cfl6wFwrw%3D%3D.pngekEw6YafVizv5cfl6wFwrw%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

0 Likes
0
5146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:10 AM . Last Modified: ‎2024-02-29 10:50 PM

You're welcome!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore