Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

DC Imbalance fault on Smart-UPS 2200 Rack Mount

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • DC Imbalance fault on Smart-UPS 2200 Rack Mount
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:10 AM . Last Modified: ‎2024-03-13 03:13 AM

0 Likes
2
1760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:10 AM . Last Modified: ‎2024-03-13 03:13 AM

DC Imbalance fault on Smart-UPS 2200 Rack Mount

I have been informed via tech support that I have a DC imbalance fault with my SUA2200RM2U Smart-UPS 2200.
The symptoms are all the left side LED lights are flashing ( 5 green Load, 2 amber AVR Trim & Boost, and the green On Line).

I have performed all the instructed methods to reset, kill the brain and revive and the cold start. Which is what brought me, to it must be a DC Imbalance fault as per the techs.

One tech instructed to replace the batteries, after some thought I decided to get a second opinion and the 2nd tech is suggesting repair and or possible replacement.

I guess I am now looking for any suggestions to resolve from the APC forums, maybe someone out there who has encountered the same issue.

Any help and or input will be greatly appreciated.

Regards,
G

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:10 AM . Last Modified: ‎2024-03-13 03:13 AM

0 Likes
0
1760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:10 AM . Last Modified: ‎2024-03-13 03:13 AM

Hi Chris,

Unfortunately the notes sound like what one of the phone techs interpreted to be the case.

History:
1. So. Calif encountered a major power outage a few weeks back.
2. My unit was and has always worked just fine.
3. When the power went out our two servers ran on the battery supply for approximately 30 minutes, I shut them and all the networking devices down as we were informed that power would not be restored for hours.
4. At this point nothing was taking any load on the APC unit.
5. The power was restored several hours later and when I arrived the next morning the unit was charging.
6. The only odd thing was that the alarm was sounding, I shut the unit off a couple of times but the alarm would not go off.
7. After a few hours my office and I were tired of hearing it and I shut it down and unplugged from the power source.
8. Over the weekend I powered the unit back up and at my surprise the alarm was off and the charging led's were on, Great! everything is back to normal.
9. I left the unit charging with no load of any kind overnight and returned the next morning to find all the left side lights flashing, and no of the right side lights were lit at all.
10. Hence this is where I am now at, the sound the tech heard was the self test and it has always done this when it is turned on, once the load test is done there is no buzzing.

Anyway, that's my story and I appreciate any and all comments.
I would really like some input on what the term DC Imbalance means in a non electrical geek way.

Regards,
G

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:10 AM . Last Modified: ‎2024-03-13 03:13 AM

0 Likes
0
1760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:10 AM . Last Modified: ‎2024-03-13 03:13 AM

I was actually able to bring up your case and i would recommend replacing the UPS. Based on the notes, I see the unit was making a loud buzzing noise and was showing an overload with no load plugged in. This is not normal behavior and a new battery would not fix this. I apologize that you have been given inconstant information. If there anyone else has any recommendations, feel free to reply.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:10 AM . Last Modified: ‎2024-03-13 03:13 AM

0 Likes
0
1761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:10 AM . Last Modified: ‎2024-03-13 03:13 AM

Hi Chris,

Unfortunately the notes sound like what one of the phone techs interpreted to be the case.

History:
1. So. Calif encountered a major power outage a few weeks back.
2. My unit was and has always worked just fine.
3. When the power went out our two servers ran on the battery supply for approximately 30 minutes, I shut them and all the networking devices down as we were informed that power would not be restored for hours.
4. At this point nothing was taking any load on the APC unit.
5. The power was restored several hours later and when I arrived the next morning the unit was charging.
6. The only odd thing was that the alarm was sounding, I shut the unit off a couple of times but the alarm would not go off.
7. After a few hours my office and I were tired of hearing it and I shut it down and unplugged from the power source.
8. Over the weekend I powered the unit back up and at my surprise the alarm was off and the charging led's were on, Great! everything is back to normal.
9. I left the unit charging with no load of any kind overnight and returned the next morning to find all the left side lights flashing, and no of the right side lights were lit at all.
10. Hence this is where I am now at, the sound the tech heard was the self test and it has always done this when it is turned on, once the load test is done there is no buzzing.

Anyway, that's my story and I appreciate any and all comments.
I would really like some input on what the term DC Imbalance means in a non electrical geek way.

Regards,
G

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore