The self-test scheduler currently offers up 4 options for scheduling; Never, Every 7 Days, Every 14 Days, UPS Startup. Is it possible, either through the Web GUI or PowerChute to further customize this schedule?
We got Smart-UPS RT 5000 XL units at several remote locations and I would like to be able to schedule them all to do their self-tests on the same day each month.
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:55 AM . Last Modified: 2024-02-14 10:37 PM
Hi,
There is not a scheduler built into the network card but if you are familiar with script writing and SNMP you can script the test to run when you would like. I have used a free app named SnmpSet.exe to set SNMP via command line. The command used to run a self-test is SnmpSet.exe -q -r:NMC IP -c:private -o:.1.3.6.1.4.1.318.1.1.1.7.2.2.0 -val:2 -tp:int
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:55 AM . Last Modified: 2024-02-14 10:37 PM
Hi,
There is not a scheduler built into the network card but if you are familiar with script writing and SNMP you can script the test to run when you would like. I have used a free app named SnmpSet.exe to set SNMP via command line. The command used to run a self-test is SnmpSet.exe -q -r:NMC IP -c:private -o:.1.3.6.1.4.1.318.1.1.1.7.2.2.0 -val:2 -tp:int
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of