Smart-UPS 750 loses connection

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 750 loses connection
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:54 AM . Last Modified: ‎2024-02-14 10:37 PM

0 Likes
4
1918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:54 AM . Last Modified: ‎2024-02-14 10:37 PM

Smart-UPS 750 loses connection

Hi all,

Hope someone can help with this.

We have a Smart-UPS 750 which for some reason keeps loosing communication and then re-establishes connection anything from 1 to 5 minutes later. Its seems to happen once a week on no particular day, however it is always between 1am and 1.30am.

The UPS is connected via a USB cable to a USB port of the back of the Dell Poweredge Server. Its been disconnected and reconnected but still no luck.

Battery was replaced only a few months ago and this problem has only started happening since start of November.

Any help appreciated with this.

Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 750
  • communication
  • connection
  • loses
  • same
  • server
  • smart-ups
  • time
  • usb
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:55 AM . Last Modified: ‎2024-02-14 10:37 PM

0 Likes
0
1916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:55 AM . Last Modified: ‎2024-02-14 10:37 PM

Hi,

Well to try and fix my issue, I am going to try and go for a firmware update on the UPS itself - http://www.apc.com/site/support/us/en/

We discovered a leaky battery about 9 months ago - So if this firmware update doesn't fix it, then who knows what untold damage the battery acid has done. In saying that, the fault only started happening 6 months AFTER the battery was changed - There is no real consistency in trying to determine the fault here.

If the firmware update doesn't fix it, I will be sending down another UPS (Im on one site, the UPS in question is on another site) and see if the same comms loss happens again.

Will let you know how it goes

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:54 AM . Last Modified: ‎2024-02-14 10:37 PM

0 Likes
0
1918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:54 AM . Last Modified: ‎2024-02-14 10:37 PM

Hey Pritesh,

What is the model number of that unit? Also do you have the serial? They can be located on the back of the unit on a bar code label.

Know what exactly what Smart-UPS you are deal with this will be key.

Tom

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:54 AM . Last Modified: ‎2024-02-14 10:37 PM

0 Likes
0
1918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:54 AM . Last Modified: ‎2024-02-14 10:37 PM

Hi Tom,

This unit is at a remote site. Logging onto the PowerChute console gives me the below info:

Smart-UPS 750
SMT750RMI2U
UPS 06.3 / MCU 11.0 (18 - 4)
AS1107222870
Hope that helps

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:54 AM . Last Modified: ‎2024-02-14 10:37 PM

0 Likes
0
1918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:54 AM . Last Modified: ‎2024-02-14 10:37 PM

I am facing the same sort of problem. We recently purchased a Smart-UPS 750, 230V. Installed the powerchute 9.2 version.

It is supporting a single server running windows 2012 server R2 foundation, with AD, print server and file server functionalities.

Initially when I installed the Powerchute version that came on the CD (9.1) the UPS was not detected whether via USB or otherwise.

I uninstalled the 9.1 version, downloaded the latest Powerchute for Win 2012 Server, and installed.

I removed the USB cable and started using the COM cable provided in the package of the UPS, since with the USB cable I was getting no communication.

The software detected the UPS fine and begun to work.

Then suddenly after 8 hours I got an email from the Powerchute monitoring agent stating the agent had lost connection.

That was 4 days ago.

Since then, I have restarted the software, stopped and started the services and agents, rebooted the server, and nothing.

I have plugged and unplugged the COM cable from the server, and from the UPS and nothing.

I have also tried by disabling the firewall (windows), have added exceptions to the firewall to ensure the software can communicate properly, and still nothing.

I am at a loss of ideas, I do have a spare COM cable from another 750 and will try that just to ensure it is not something wrong with the cables supplied.

The server OS has the latest updates available installed up to the 8th of Jan 2016.

After those updates where installed the server had to reboot several times, and Powerchute allways came back up and worked fine after each reboot, detecting the UPS, talking to it and providing reports, etc...

Then when all was done and the server had been running for more than 8 hours, the agent simply stopped with no reason whatsoever.

Any and all help greatly appreciated, as Im starting to feel a chill down my spine that something might go wrong and the UPS will not do its job, and shut down the server in a timely and proper fashion causing a disaster scenario, that Id really not have to go through.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:55 AM . Last Modified: ‎2024-02-14 10:37 PM

0 Likes
0
1917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:55 AM . Last Modified: ‎2024-02-14 10:37 PM

Hi,

Well to try and fix my issue, I am going to try and go for a firmware update on the UPS itself - http://www.apc.com/site/support/us/en/

We discovered a leaky battery about 9 months ago - So if this firmware update doesn't fix it, then who knows what untold damage the battery acid has done. In saying that, the fault only started happening 6 months AFTER the battery was changed - There is no real consistency in trying to determine the fault here.

If the firmware update doesn't fix it, I will be sending down another UPS (Im on one site, the UPS in question is on another site) and see if the same comms loss happens again.

Will let you know how it goes

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.