Critical - UPS: At least one faulty battery exists - But which???

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Critical - UPS: At least one faulty battery exists - But which???
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
117
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 07:33 AM

0 Likes
3
6094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 07:33 AM

Critical - UPS: At least one faulty battery exists - But which???

 

There are four battery packs in this unit, they were changed out only a few months ago yet I keep getting these warnings again.

 

Name     : Smart UPS 10000

Location : xxx

Contact  : xxx

https://APC10K.mydomain.com

https://192.168.1.253

Serial # : ZA0443007046

Device Ser #: YS0451110605 

Date: 04/20/2014

Time: 23:26:14

Code: 0x0119

Critical - UPS: At least one faulty battery exists.

 

 
Smart-UPS RT 10000 RM XL: UPS_AZ
 
  Critical Alarm Replacement Battery Needed
At least one faulty battery exists.
  Critical Alarm Self-Test Failed
Failed a self-test.
 
 
Quick Status
 
Load in Watts Battery Capacity
 
 
 
 
 
 
42.0 %
 
 
 
 
 
100.0 %
 
 
Input Voltage: 247.6 VAC
Output Voltage: 208.2 VAC
 
Runtime Remaining: 21 minutes
Last Battery Transfer: Due to software command or UPS's test control

 

 

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:13 AM

0 Likes
0
6083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:13 AM

Speaking from hands on experience it can sometimes be challenging to determine which battery modules are bad with these RT UPS. An RBC44 ( two skinny modules) counts as one string because the two modules ( nominally 96 volts per Angela N's post) are in series with each other - IE connected end to end like Christmas lights. Inside the RT10000 UPS itself there two 192 volt strings in parallel with each other. In the external battery modules (also having two RBC44's / 4 skinny modules) it is the same. Having access and knowing how to use a DVM (digital multimeter) is almost essential, as you can use it to measure the voltage at the black battery connectors for each module (either when plugged in to the UPS, or unplugged).

If you have a multimeter and know how to use it, with the battery modules plugged into the UPS, measure the DC terminal voltage between pairs of adjacent batteries. If the batteries are relatively healthy you should measure about 108 to 109 Volts DC at each module...differences of a half to one volt or so are ok. If one or the other module has one or two cells going bad inside, you will see an imbalance Eg you might see 111 to 113 or 114 volts across one, and 103 to 105 or 106 volts across the other. After that the next step is to disconnect the cells and measure the voltage at the battery connector (while loose) and see what it is. On a healthy fully charged module the voltage should be around 103 to 104 volts DC. The module with the lower voltage usually is the one going bad, but sometimes its the opposite, as dying cells inside the module can sometimes be overcharged by the UPS and show a higher than normal voltage.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:13 AM

0 Likes
0
6083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:13 AM

Status
Last Battery Transfer:Due to software command or UPS's test control
Internal Temperature:95.3°F
Runtime Remaining:21 minutes
Power
Input Voltage:247.6 VAC
Output Voltage:208.2 VAC
Input Frequency:59.99 Hz
Load
Load Power:42.0 %Watts
Apparent Load Power:35.0 %VA
Load Current:16.87 Amps
Battery
Capacity:100.0 %
Battery Voltage:214.9 VDC
External Batteries:1

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:13 AM

0 Likes
0
6083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:13 AM

Hi again!

This UPS does not have "intelligent" batteries so which ones did you not replace last time? I forgot if you had external batteries, like an external SURT192XLBP battery pack or if you're just talking about the (2) RBC44 - which are four "strings" which go inside the unit. Assuming it is just the (2) RBC44 - four strings/modules internal to the UPS, sometimes it can just be one or two strings that have a problem or all of them. The first thing we'd ask in this situation is to verify the environment that this UPS is in to see if this has somehow contributed to a premature battery failure. Otherwise, I don't think there will be much to do to really narrow down the string(s) and doing in depth testing to see if there is just a bad 12V battery inside the 96V string. This is not something we typically have users do but some advanced users choose to do it.

Depending on what you found in the environment or at the battery string level, and if these were genuine APC RBC44's, technical support could replace one or both of them under warranty since APC batteries have a (1) year warranty on themselves.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:13 AM

0 Likes
0
6084
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:12 AM . Last Modified: ‎2024-03-12 03:13 AM

Speaking from hands on experience it can sometimes be challenging to determine which battery modules are bad with these RT UPS. An RBC44 ( two skinny modules) counts as one string because the two modules ( nominally 96 volts per Angela N's post) are in series with each other - IE connected end to end like Christmas lights. Inside the RT10000 UPS itself there two 192 volt strings in parallel with each other. In the external battery modules (also having two RBC44's / 4 skinny modules) it is the same. Having access and knowing how to use a DVM (digital multimeter) is almost essential, as you can use it to measure the voltage at the black battery connectors for each module (either when plugged in to the UPS, or unplugged).

If you have a multimeter and know how to use it, with the battery modules plugged into the UPS, measure the DC terminal voltage between pairs of adjacent batteries. If the batteries are relatively healthy you should measure about 108 to 109 Volts DC at each module...differences of a half to one volt or so are ok. If one or the other module has one or two cells going bad inside, you will see an imbalance Eg you might see 111 to 113 or 114 volts across one, and 103 to 105 or 106 volts across the other. After that the next step is to disconnect the cells and measure the voltage at the battery connector (while loose) and see what it is. On a healthy fully charged module the voltage should be around 103 to 104 volts DC. The module with the lower voltage usually is the one going bad, but sometimes its the opposite, as dying cells inside the module can sometimes be overcharged by the UPS and show a higher than normal voltage.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of