Critical - UPS: An input voltage or frequency problem prevents switching to bypass mode.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Critical - UPS: An input voltage or frequency problem prevents switching to bypass mode.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
belostenac
belostenac
Cadet

Posted: ‎2022-10-11 01:45 AM

1 Like
1
2529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-11 01:45 AM

Critical - UPS: An input voltage or frequency problem prevents switching to bypass mode.

In the last few weeks, the UPS MGE Galaxy 3500 40 kVA very often logs the event: Critical - UPS: An input voltage or frequency problem prevents switching to bypass mode. After a few seconds/minutes the error disappears and the message appears: Informational - UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

 

I suspect the problem is with the input voltage, which I would say from the logs is too high (log file attached).

 

What should we pay attention to and is there anything we could do to prevent similar events?

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2022-10-11 06:18 AM

1 Like
0
2516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-11 06:18 AM

Hi,

 

You are correct. This is likely due to the input voltage or frequency moving outside the acceptable range where bypass operation is supported but not enough to cause the UPS to transfer to battery operation. On the voltage side this is somewhere between +/- 10% and +/- 20% of the nominal input. The range of operation related to the frequency can be configured via the display (note: changes can only be made if the UPS output power is off). I believe that the default setting is +/- 10Hz but it can also be set for .1 Hz  or 3Hz. If your setting is something other than 10 then perhaps changing the setting could reduce the number of instances of the event.

 

When this event is active, the UPS would not be able to transfer to bypass if maintenance is required or if a fault were to occur which prevented the UPS running in normal operation.  Since this event is triggered by the utility voltage you would have to address this with either your site facilities personnel or with your local utility provider. 

 

I hope this helps. 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2022-10-11 06:18 AM

1 Like
0
2517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-11 06:18 AM

Hi,

 

You are correct. This is likely due to the input voltage or frequency moving outside the acceptable range where bypass operation is supported but not enough to cause the UPS to transfer to battery operation. On the voltage side this is somewhere between +/- 10% and +/- 20% of the nominal input. The range of operation related to the frequency can be configured via the display (note: changes can only be made if the UPS output power is off). I believe that the default setting is +/- 10Hz but it can also be set for .1 Hz  or 3Hz. If your setting is something other than 10 then perhaps changing the setting could reduce the number of instances of the event.

 

When this event is active, the UPS would not be able to transfer to bypass if maintenance is required or if a fault were to occur which prevented the UPS running in normal operation.  Since this event is triggered by the utility voltage you would have to address this with either your site facilities personnel or with your local utility provider. 

 

I hope this helps. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore