UPS: In temporary bypass.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS: In temporary bypass.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
JasonNaughton
Crewman JasonNaughton
Crewman

Posted: ‎2022-10-04 05:51 PM . Last Modified: ‎2022-10-04 05:59 PM

1 Like
5
1417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-04 05:51 PM . Last Modified: ‎2022-10-04 05:59 PM

UPS: In temporary bypass.

Hi All,

 

I have a Symetra LX 16000 and tonight I got the following event that occurred and disappeared within seconds:

 

10/04/202220:24:32UPS: Returned from temporary bypass.
10/04/202220:24:24UPS: In temporary bypass.

 

I'm looking at the logs and I don't see any reason why the UPS decided to go into "temporary bypass"  There are no alarms and the UPS is OnLine.   The UPS is lightly loaded:

 

Measurements
Last Battery Transfer: Due to software command or UPS's test control
Internal Temperature: 36.0°C
Runtime Remaining: 7hr 20min
 
Input Power
 Phase L1Phase L2Phase L1/L2
Input Voltage121.1 VAC121.1 VAC209.5 VAC @ 59.99Hz
 
Output Power
 Phase L1Phase L2Phase L1/L2
Output Voltage121.1 VAC120.2 VAC211.3 VAC @ 59.98Hz
Output Current09.4 Amps13.4 Amps---
Output Load kVA01.13 kVA01.68 kVA---
Output Watts at n+0015 %Watts026 %Watts---
Output VA at n+0012 %VA018 %VA---
 
Fault Tolerance
Redundancy: n+3
Present kVA Capacity: 16.0 kVA
 
As you can see the UPS is very lightly loaded.  Yes there is an imbalance between the two phases but it's not much of an imbalance.   When I dug into the logs I don't see any reason why the UPS would have done this during this time frame:
 
Date Time Vmin1 Vmin2 Vmax1 Vmax2 Vout1 Vout2 Iout1 Iout2 %Wout1 %Wout2 kVAout1 kVAout2 %VAout1 %VAout2 Freq %Cap Vbat TupsC T1ambC %Hum1 T2ambC %Hum2 
 10/04/2022  20:39:11  121.1  120.2  121.1  121.1  121.1  120.2  9.4  13.4  16  26  1.13  1.68  12  18  60.00  100.0  138.7  36.0  19.0          
 10/04/2022  20:29:11  121.1  120.2  121.1  121.1  121.1  120.2  9.4  13.4  16  25  1.13  1.66  12  18  60.01  100.0  138.7  35.0  19.0          
 10/04/2022  20:19:11  120.2  120.2  121.1  121.1  121.1  120.2  9.4  13.4  15  26  1.13  1.67  12  18  60.00  100.0  138.7  36.0  19.0          
 10/04/2022  20:09:11  120.2  120.2  121.1  120.2  121.1  120.2  9.4  13.4  16  26  1.13  1.69  12  18  59.99  100.0  138.7  35.0  19.0          

 

If someone could directly to information regarding this event it would be appreciated...

 

Cheers

 

Jason 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-10-10 04:00 PM

0 Likes
4
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-10 04:00 PM

Hi @JasonNaughton 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.  I am sorry to hear about the issue that you are having.

 

From the PowerView/LCD of the UPS you'll be able to view what are the events that the UPS has captured.  You can press the ESC key and navigate to Diags > Faults and Diagnostics and also Logging > View Log.

 

Downloading the NMC log files can also help us further diagnose on what has happened on the UPS.

 

Status >> UPS >> Measurements >>Take a screen shot

Status >> UPS >> Power >> Take a screen shot

Status >> UPS >> Battery >> Main Frame >> Take a screen shot
Status >> UPS >> Battery >> XR1 / Battery Frame 2>> Take a screen shot
Status >> UPS >> Battery >> [View All Battery Raw Status Data] >> Take a screen shot

Status >> UPS >> Intelligence Modules >>Take a screen shot
Status >> UPS >> Intelligence Modules >> [View System Raw Status Data]

 

Kindly download the debug.tar from the NMC menu: About > Support > Generate Logs > Download

 

If you do not have access to the network management card, the same information can be gathered through the LCD and it would help if you can take photos of the RSDs.

 

  • Retrieve the Intelligence Module Raw Status Data (RSD) from the LCD by hitting the ESC key and then navigating to Intelligence Module.  Gather the FW version, SN, and Raw Status Data.
  • Retrieve the Power Module Raw Status Data (RSD) from the LCD by hitting the ESC key and then navigating to Power Module.  Gather the SN and Raw Status Data.
  • Retrieve the Battery Module Raw Status Data (RSD) from the LCD by hitting the ESC key and then navigating to Battery Module.  Gather the SN and Raw Status Data.

 

Please send the screenshots and the debug.tar to us through DM or by reaching out to the Technical Support team of your Country.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JasonNaughton
Crewman JasonNaughton
Crewman

Posted: ‎2022-10-12 11:51 AM

In response to JonPro
0 Likes
3
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-12 11:51 AM

Hello Jon,

 

I've DM'd the images and log file to you.  Just so your aware, I've disconnected the 3rd and 4th Runtime frames and removed any batteries from the frames that were older than 2018.   I also re-seated the power modules as per a suggestion from Schneider.  These events will show up in the event log.

 

Cheers

 

Jason

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-10-13 05:05 PM

In response to JasonNaughton
0 Likes
2
1334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-13 05:05 PM

Hi @JasonNaughton 

 

With the screenshots that you have provided, it looks like the UPS had a hiccup, did it cause any service disruption?  I have also replied to your DM.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JasonNaughton
Crewman JasonNaughton
Crewman

Posted: ‎2022-10-13 05:48 PM

In response to JonPro
0 Likes
1
1329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-13 05:48 PM

Hi Jon,

 

No there was no disruption thank goodness.  The temporary bypass only lasted 8 seconds and the line power was in place so there was no outage.  What concerned me was what caused the UPS to go into temporary bypass?   Thank goodness there was no power outage that just may have happened at the same time.   

 

I have noticed that in Frame #2 there are negative signs in-front of the raw battery data.  Can you decipher what this means?   I reached out to Schneider to attempt to diagnose the possible issue.    They suggested pulling any of the batteries that were older than 2016.   Disconnecting the XR frames that no longer had batteries in them, and to reseat each power module.   I did all of that but I’m not sure any of that may have resolved whatever issue caused the UPS to put itself into bypass.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-10-13 07:02 PM

In response to JasonNaughton
0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-13 07:02 PM

Hi @JasonNaughton 

 

You can disregard the negative (-) sign on the RSDs, I have sent you an invite to where you can upload the debug file.  From the LCD, you can also go to fault and diagnostics and logs to review the events.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of