Configure PowerChute 8.0.1.609 to shutdown Windows Server 2003 but keep UPS
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0101:22 AM. Last Modified: 2024-03-0601:49 AM
Configure PowerChute 8.0.1.609 to shutdown Windows Server 2003 but keep UPS
I have a SmartUPS 1500 SUA1500I running both a windows server 2003 box (powerchute 8.0.1.609 connected by USB) and a telephone switch (not connected to UPS management, only running from the power output)
I wish to configure the UPS to run as normal for 15 minutes. After this i wish the server to be shut down but the UPS to remain active until its battery is depleted. How do I configure this in powerchute?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0101:22 AM. Last Modified: 2024-03-0601:49 AM
Good day rhyds,I suggest that you use Powerchute Network Shutdown (works with a network management card installed in the UPS) instead of Powerchute Business Edition. Because with PCBE, the UPS is commanded to go to low voltage sleep mode after the server gracefully shuts down.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0101:22 AM. Last Modified: 2024-03-0601:49 AM
Good day rhyds,I suggest that you use Powerchute Network Shutdown (works with a network management card installed in the UPS) instead of Powerchute Business Edition. Because with PCBE, the UPS is commanded to go to low voltage sleep mode after the server gracefully shuts down.