Config.ini via DHCP limitations?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Config.ini via DHCP limitations?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:53 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
12
2563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:53 AM . Last Modified: ‎2024-03-05 12:06 AM

Config.ini via DHCP limitations?

I'm having trouble getting a config.ini file to fully process when it's supplied over FTP with DHCP options 66 and 67.  It seems like it gets part of the way through the file and then stops processing for some reason and I can't seem to figure out why.  If I manually FTP the file to the device it seems to process just fine.

The first time the config.ini gets transferred I see this in the log:

07/22/201406:29:48System: Warmstart.
07/22/201405:28:44System: Restarting. FTP boot file download.
07/22/201405:28:42System: Configuration file upload complete, with 27 valid values.
07/22/201405:28:42System: Configuration change. Email 'from' address.
07/22/201405:28:42System: Configuration change. Temperature preference.
07/22/201405:28:42System: Configuration change. Secondary NTP server address.
07/22/201405:28:42System: Configuration change. Primary NTP server address.
07/22/201405:28:41System: Configuration change. NTP enable.
07/22/201405:28:41System: Configuration change. Secondary RADIUS server secret.
07/22/201405:28:41System: Configuration change. Secondary RADIUS timeout.
07/22/201405:28:40System: Configuration change. Secondary RADIUS server address.
07/22/201405:28:40System: Configuration change. Primary RADIUS server secret.
07/22/201405:28:40System: Configuration change. Primary RADIUS timeout.
07/22/201405:28:40System: Configuration change. Primary RADIUS server address.
07/22/201405:28:39System: Configuration change. RADIUS access.
07/22/201405:28:39System: Configuration change. System inactivity timeout.
07/22/201405:28:39System: Configuration change. System contact.
07/22/201405:28:38System: Configuration change. Override Manual DNS Settings.
07/22/201405:28:38System: Configuration change. IPv6 enable.
07/22/201405:28:38System: Configuration change. Domain name.

The next time it renews it's DHCP lease and gets the same config.ini I get this:

07/22/201406:39:01System: Warmstart.
07/22/201406:38:49System: Restarting. FTP boot file download.
07/22/201406:38:49System: Configuration change. System contact.
07/22/201406:38:49System: Configuration change. Override Manual DNS Settings.
07/22/201406:38:48System: Configuration change. IPv6 enable.
07/22/201406:38:48System: Configuration change. Domain name.
07/22/201406:38:47System: Configuration change. System administrator password.
07/22/201406:38:47System: Configuration file upload complete, with 0 valid values.
07/22/201406:38:47System: File transfer failed.

The third time I get this:

07/22/201407:00:29System: Warmstart.
07/22/201407:00:17System: Restarting. FTP boot file download.
07/22/201407:00:16System: Configuration file upload complete, with 0 valid values.
07/22/201407:00:16System: File transfer failed.

I'm not sure why it's reporting "File transfer failed" because on the FTP server it looks the same every time it connects.

(000022)7/22/2014 9:04:15 AM - (not logged in) (10.11.12.13)> Connected, sending welcome message...

(000022)7/22/2014 9:04:15 AM - (not logged in) (10.11.12.13)> 220 Test FTP FileZilla Server version 0.9.45 beta

(000022)7/22/2014 9:04:15 AM - (not logged in) (10.11.12.13)> USER apc

(000022)7/22/2014 9:04:15 AM - (not logged in) (10.11.12.13)> 331 Password required for apc

(000022)7/22/2014 9:04:15 AM - (not logged in) (10.11.12.13)> PASS ***

(000022)7/22/2014 9:04:15 AM - apc (10.11.12.13)> 230 Logged on

(000022)7/22/2014 9:04:15 AM - apc (10.11.12.13)> TYPE I

(000022)7/22/2014 9:04:15 AM - apc (10.11.12.13)> 200 Type set to I

(000022)7/22/2014 9:04:16 AM - apc (10.11.12.13)> PORT 10,35,14,84,11,184

(000022)7/22/2014 9:04:16 AM - apc (10.11.12.13)> 200 Port command successful

(000022)7/22/2014 9:04:16 AM - apc (10.11.12.13)> RETR apc-config.ini

(000022)7/22/2014 9:04:16 AM - apc (10.11.12.13)> 150 Opening data channel for file download from server of "/apc-config.ini"

(000022)7/22/2014 9:04:16 AM - apc (10.11.12.13)> 226 Successfully transferred "/apc-config.ini"

(000022)7/22/2014 9:04:17 AM - apc (10.11.12.13)> QUIT

(000022)7/22/2014 9:04:17 AM - apc (10.11.12.13)> 221 Goodbye

(000022)7/22/2014 9:04:17 AM - apc (10.11.12.13)> disconnected.

If I manually FTP the same config.ini file to the device it seems to process it just fine.  I'm wondering if maybe there is some kind of limitation on the size of the file or maybe something with the encoding that is causing it to blow up.  Is there any detailed config.ini processing log available or anything else that might help me figure this out? 

The device is a Smart-UPS 1500, here are the software versions:

Model Number:AP9630
Hardware Revision:05
Manufacture Date:11/19/2013

Application Module

Name:sumx
Version:v5.1.3
Date:May 4 2010
Time:14:06:35

APC OS (AOS)

Name:aos
Version:v5.1.3
Date:May 4 2010
Time:13:55:26

APC Boot Monitor

Name:bootmon
Version:v1.0.1
Date:Aug 3 2009
Time:16:30:40

Incidentally I tried with 6.0.6 and 6.1.1 firmware but that was even worse, the device got stuck in a reboot loop.  It would ftp the file, process it, reboot and then do it all over again until I stopped the FTP server so it couldn't get the file again.  At least after downgrading to the older version it only gets the file when it renews it's DHCP lease.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • config.ini
  • dhcp
  • NMC
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

I apologize. I got wrapped up the last two days and found out last Thursday we are able to replicate your issues on NMC2. We don't actively develop on the older NMC1 platform anymore so any fixes would go into NMC2 v6.X.X platform. We were going to be trying it the latest available development code and if not fixed there, entering a bug request to address this issue with using the bootfile.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

Have you tried 5.1.7? That is our latest version of the v5.X.X code. Meanwhile, I am going to see if someone with the resources to test this can look at it.


There are no extra log files you are missing and I know of no limitations. The only thing related to this I was aware of was on our older cards and TFTP (versus FTP) not working properly for this functionality.

I would try 5.1.7 to verify it reacts the same way as 5.1.3 and I will see what other information I can find out in the meantime. I will attached 5.1.7 to the post if you need it.

Attachments
apc_hw05_aos517_sumx517_bootmon102.exe.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

Pretty much the same results.  It processes some of the config.ini but not all of it and it still says the file transfer failed.

Is it possible the file encoding is wrong?

07/22/201413:10:12System: Network Interface restarted.
07/22/201413:09:59System: Restarting. FTP boot file download.
07/22/201413:09:59System: Configuration change. Override Manual DNS Settings.
07/22/201413:09:59System: Configuration change. IPv6 enable.
07/22/201413:09:59System: Configuration change. Domain name.
07/22/201413:09:58System: Configuration file upload complete, with 0 valid values.
07/22/201413:09:58System: File transfer failed.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

It seems to get a few of the settings the 2nd time it downloads the file too.  I thought I was seeing this in the logs before but I figured I was misreading it.

07/22/201413:20:38System: Restarting. FTP boot file download.
07/22/201413:20:38System: Configuration file upload complete, with 26 valid values.
07/22/201413:20:38System: Configuration change. SNMP access control 2 community.
07/22/201413:20:38System: Configuration change. SNMP access control 1 community.
07/22/201413:20:37System: Configuration change. Temperature preference.
07/22/201413:20:37System: Configuration change. Secondary NTP server address.
07/22/201413:20:37System: Configuration change. Primary NTP server address.
07/22/201413:20:37System: Configuration change. NTP enable.
07/22/201413:20:36System: Configuration file upload complete, with 0 valid values.
07/22/201413:20:36System: File transfer failed.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

Yes, this is strange. I can't answer much more without having someone look into it for me and test it. I expect a response to help provide responses to you hopefully in a few days to see if we can replicate the problem and figure out what it is wrong on both firmwares (v5 and v6). I feel like something is stopping it from applying all of the values but it's only a guess at this point.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

It seems to be cutting off the file somehow.  The last file I tested it quit at 1460 characters (I know this because it cut off one of the settings in mid string.)  I tried Filezilla FTP server and the IIS FTP server and neither one worked properly.  I also did a wireshark capture and it shows that the entire file was transferred so I'm pretty sure it's something on the device end. 

As an aside I see from the capture that it is trying a TFTP transfer first then going to FTP, that's probably why it always shows "file transfer failed" in the logs first.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

Yup, it does try TFTP first then FTP. That was where I knew we had a bug on the older cards that TFTP did not work at all.

I will keep you updated and thank you for the extra information, it is appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

I appreciate the attention to this issue very much, thank you!

I put a TFTP server up and it consumes the same INI file and processes all of the settings successfully so it's something about the FTP code apparently.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

Just an FYI, I expect to know something early next week between the testing team's previous obligations (an all week training) and time to review/look at it. Will report back ASAP!

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

That's great, thanks!  I may have stumbled across another issue that's in the same neighborhood but not quite the same.  Testing on a Smart-UPS 5000 RM XL with an AP9617 running AOS v3.7.3 and SUMX v3.7.2 I can't seem to get the thing to take ANY config from the DHCP setup and it never tries TFTP.  Did you say that there was some kind of FTP issue with some earlier hardware?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

Yeah, there is. Here is some information:

Issue

Network Management Card 1 (AP9617/18/19) not attempting a TFTP transfer of a configuration/boot file while using BOOTP


Product Line

  • Network Management Card 1 (NMC1) - AP9617, AP9618, AP9619

Devices with an embedded Network Management Card 1 include (but are not limited to): Metered/Switched Rack PDUs (AP78XX, AP79XX), Rack Automatic Transfer Switches (AP77XX, Environmental Monitoring Units (AP9320, AP9340, Netbotz 200)

Environment

  • All serial numbers
  • Firmware versions 3.X.X

Cause

In the user's manual for Network Management Card 1 (AP9617, AP9618, AP9618), the following feature set of the NMC is noted:

When the Management Card reboots, the BOOTP server provides it with the TCP/IP settings.
• If you specified a bootup file name, the Management Card attempts to transfer that file from the BOOTP server using TFTP or FTP.

The Management Card assumes all settings specified in the bootup file. In NMC firmware revisions 1.x and 2.x, this feature works as designed. While using an NMC with BOOTP to assign an IP address, the NMC will accept an IP address from a BOOTP server, and five minutes later, attempt a TFTP transfer of a specified bootup file. If no TFTP server is reachable, it will attempt FTP transfer of a specified bootup file.

In NMC firmware revision 3.x, the NMC does not attempt a TFTP transfer, only an FTP transfer. Customers relying on TFTP will not have success in specifying a bootup file.


Resolution

Though TFTP does not work, customers can use FTP to configure their NMC device using a boot file (config.ini). FTP normally requires a client login. Since the NMC device is at its default settings, the customer will need to create an "apc" user on the FTP server. At default settings, the NMC device will attempt an FTP login using apc for both the username and password. The customer will need to create such an account on their FTP server in order for a successful upload of the boot file.

I think this was discovered after those cards were discontinued so that is why it was not addressed. So TFTP does not work but FTP should with the older cards.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

I'm beginning to wonder if I'm chasing a pipe dream here.  The second (older) UPS doesn't seem to even try TFTP (as the article described) but it does get the file from the FTP server OK and then doesn't do anything with it.

07/25/201413:51:57System: Warmstart.
07/25/201413:51:39System: File transfer failed.

I've tried 3 different FTP servers now and they all show the same thing - ups logs in, ups downloads config.ini, ups disconnects.  Once again if I manually FTP the file TO the UPS it processes it just fine.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:54 AM . Last Modified: ‎2024-03-05 12:06 AM

I apologize. I got wrapped up the last two days and found out last Thursday we are able to replicate your issues on NMC2. We don't actively develop on the older NMC1 platform anymore so any fixes would go into NMC2 v6.X.X platform. We were going to be trying it the latest available development code and if not fixed there, entering a bug request to address this issue with using the bootfile.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.