Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Clarification on definitions of terms

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Clarification on definitions of terms
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

0 Likes
2
1011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

Clarification on definitions of terms

Hi,
I realise that this is the ultimate noobie question (or series of questions) but I have some APC terminology and I was wondering if someone could elaborate on what they actually mean in the real world when it comes to choosing a UPS.
We have 2 Smart-APC UPSs at the moment and we plan to upgrade at least one of them. I have checked the values for the fields in Powerchute so that we might make an informed decision but the obscure definitions which I have found on the web make it difficult to decide which values we should be watching out for when choosing which UPS should be replaced. So here goes, I have included the definitions which I have located thus far.

Capacity - The UPS has a nominal maximum capacity, usually indicated by the number in its model name. In this example, it is 650 VA. The UPS will probably handle a load slightly above this figure--much the way your car doesn't stop dead when the fuel gauge hits "E"

Load - power consumed by a circuit
PC power supplies use a technique called switching to generate their DC voltages. Due to the manner in which these sorts of power supplies function, they need to have a load, meaning something that draws power from the supply, in order to function properly. A power supply that is turned on with no load attached will either fail to function or will function improperly. Better-quality supplies will detect a no-load situation and shut down, but cheap ones can be damaged. This is why you should not "test" a power supply by just plugging it in with nothing attached to it.

Load Power - Apparent Power (I'm assuming that this is also known as Load Power) is measured in volt-amperes (VA) and is the voltage on an AC system multiplied by all the current that flows in it. It is the vector sum of the active and the reactive power.
Apparent power is measured in Volt-Amps (usually kVA) Apparent Power = Voltage x Current

Load current - the current drawn by the application that is connected to the power source
If, given the technical nature of these terms, the definitions can't be broken down any further, that's no problem. Alternatively, could you let me know which terms to pay attention when choosing which unit should be replaced?
Many Thanks,
I'd really appreciate any advice on this and again, I apologize for basically asking for a class in Electricity 101 :).
Justin.

Message was edited by: justin.forde@bankers.ie

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

0 Likes
0
1011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

Hi,
I realise that this is the ultimate noobie question (or series of questions) but I have some APC terminology and I was wondering if someone could elaborate on what they actually mean in the real world when it comes to choosing a UPS.
We have 2 Smart-APC UPSs at the moment and we plan to upgrade at least one of them. I have checked the values for the fields in Powerchute so that we might make an informed decision but the obscure definitions which I have found on the web make it difficult to decide which values we should be watching out for when choosing which UPS should be replaced. So here goes, I have included the definitions which I have located thus far.

Capacity - The UPS has a nominal maximum capacity, usually indicated by the number in its model name. In this example, it is 650 VA. The UPS will probably handle a load slightly above this figure--much the way your car doesn't stop dead when the fuel gauge hits "E"

Load - power consumed by a circuit
PC power supplies use a technique called switching to generate their DC voltages. Due to the manner in which these sorts of power supplies function, they need to have a load, meaning something that draws power from the supply, in order to function properly. A power supply that is turned on with no load attached will either fail to function or will function improperly. Better-quality supplies will detect a no-load situation and shut down, but cheap ones can be damaged. This is why you should not "test" a power supply by just plugging it in with nothing attached to it.

Load Power - Apparent Power (I'm assuming that this is also known as Load Power) is measured in volt-amperes (VA) and is the voltage on an AC system multiplied by all the current that flows in it. It is the vector sum of the active and the reactive power.
Apparent power is measured in Volt-Amps (usually kVA) Apparent Power = Voltage x Current

Load current - the current drawn by the application that is connected to the power source
If, given the technical nature of these terms, the definitions can't be broken down any further, that's no problem. Alternatively, could you let me know which terms to pay attention when choosing which unit should be replaced?
Many Thanks,
I'd really appreciate any advice on this and again, I apologize for basically asking for a class in Electricity 101 :).
Justin.

Message was edited by: justin.forde@bankers.ie

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

0 Likes
0
1011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

Hi Clarkson, Winna,
Thank you very much, your advice has become My Go-to Guide when it comes to UPS systems :).
I'm doing the maths at the moment - could you tell me 2 things -

Voltage - I'm assuming that that's Input/Output Voltage and it doesn't matter which I choose since the UPS says that they're both at the same level.
Power Factor - Is there a way that I can determine this? According to Powerchute, the batteries on our UPS systems were last replaced in 2008 and 2006 so I'm assuming that the UPS itself predates these both but I don't think that I can place the UPS system in an 'older' or 'newer' category in order to determine the Power Factor from this.

Many, many thanks, once again,
Justin.

Message was edited by: justin.forde@bankers.ie

Message was edited by: justin.forde@bankers.ie

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

0 Likes
0
1012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

Hi,
I realise that this is the ultimate noobie question (or series of questions) but I have some APC terminology and I was wondering if someone could elaborate on what they actually mean in the real world when it comes to choosing a UPS.
We have 2 Smart-APC UPSs at the moment and we plan to upgrade at least one of them. I have checked the values for the fields in Powerchute so that we might make an informed decision but the obscure definitions which I have found on the web make it difficult to decide which values we should be watching out for when choosing which UPS should be replaced. So here goes, I have included the definitions which I have located thus far.

Capacity - The UPS has a nominal maximum capacity, usually indicated by the number in its model name. In this example, it is 650 VA. The UPS will probably handle a load slightly above this figure--much the way your car doesn't stop dead when the fuel gauge hits "E"

Load - power consumed by a circuit
PC power supplies use a technique called switching to generate their DC voltages. Due to the manner in which these sorts of power supplies function, they need to have a load, meaning something that draws power from the supply, in order to function properly. A power supply that is turned on with no load attached will either fail to function or will function improperly. Better-quality supplies will detect a no-load situation and shut down, but cheap ones can be damaged. This is why you should not "test" a power supply by just plugging it in with nothing attached to it.

Load Power - Apparent Power (I'm assuming that this is also known as Load Power) is measured in volt-amperes (VA) and is the voltage on an AC system multiplied by all the current that flows in it. It is the vector sum of the active and the reactive power.
Apparent power is measured in Volt-Amps (usually kVA) Apparent Power = Voltage x Current

Load current - the current drawn by the application that is connected to the power source
If, given the technical nature of these terms, the definitions can't be broken down any further, that's no problem. Alternatively, could you let me know which terms to pay attention when choosing which unit should be replaced?
Many Thanks,
I'd really appreciate any advice on this and again, I apologize for basically asking for a class in Electricity 101 :).
Justin.

Message was edited by: justin.forde@bankers.ie

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore