Cisco 4507E with 4200w power supply
  • Cisco 4507E with 4200w power supply
Posted: ‎2021-06-28 09:11 PM . Last Modified: ‎2024-03-15 01:25 AM
1409
I have several closets with dual SmartUPS 3000 power supplies. I am planning to install Cisco Catalyst 4507E chassis using the 4200w power supplies. According to specification for this power supply
(http://www.cisco.com/en/US/prod/collateral/switches/ps5718/ps4324/product_data_sheet09186a00801f3dd9...)
To operate with needed amount of power to drive just data services (no POE) the following input is required:
"Two 12A at 100 VAC"
The APC SmartUPS 3000 a 120v UPS rated for "Max Configurable Power 2250 Watts / 3000 VA". The SmartUPS is plugged into utility power via L5-30.
So the max VA the 4500 could drawn is 12 x 100 x 2 = 2400. Which I assume means plugging both AC inputs from the 4200w power supply into a SmartUPS 3000 should not exceed the capacity of the UPS under any power draw condition.
  • 4500
  • cisco
  • smartups
hi,
your calculations are correct. the only problem is - the output of the Smart UPS is 120v. if the device has a NEMA 5-15 plug, it will be fed 120v. i'd double check on the actual wattage draw of each of the power supplies to get a more accurate measure of what you need. i tried to find it on the page but maybe i missed it.
Well I assume if the voltage was higher that would mean the amps needed would be lower. But then again I am guessing at most of this stuff. So I assumed that if it was rated at 12amps at 100v but the supply was actually 120v that the required amps would be lower? I could of course be wildly off on this point.
yeah you are right essentially. as the voltage climbs higher, less amps are required and vice versa. i'd just make sure there isnt a problem with providing the equipment more voltage even though it equals the same amount of VA.
hi,