Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Chilled water

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Chilled water
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:31 PM

0 Likes
7
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:31 PM

Chilled water

Hi,

I am interested in the InRow RC units for a small data centre that is running too hot. We currently have a 5 tonne ceiling hung A/C that runs off city water, I think in this city it is actually against the by-laws, but that's another issue all together. Since we can't "expand" the capacity of the existing unit, something like an inrow solution makes sense. The data centre is too far from the exterior of the building to install any sort of vented system, so InRow SC units are out of the question.

So, what I need to know is what solutions are available to provide chilled water for the RC units? We obviously do not have an existing chiller, so I need everything to run 1 or 2 RC units. I understand what the chiller does, I just need manufacturer names and models to support this configuration and maybe tips on whether this is a viable solution, especially from a cost perspective.

Thanks,


--Pete

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • chiller
  • cooling
  • inrow
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:30 PM

0 Likes
0
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:30 PM

Hi
From my point of view I would look through the document http://www.apcmedia.com/salestools/ASTE-6Z5S8Z_R1_EN.pdf
especially page 5.
This should help to understand how to remove hot and what the configuration could be.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:31 PM

0 Likes
0
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:31 PM

i am going to ask our cooling support team for any suggestions on this and let you know what I get.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:31 PM

0 Likes
0
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:31 PM

Hi pete,

Here is what one of the cooling team members replied with/suggested:

OK. I have a few concerns. the first is that the customer only needs two ACRC units. Do we know what the heat load of the space is? the concept of inrow cooling is vastly different from the cm unit currently being utilized. Does the facility have means to run the proper piping for CW out to a chiller? I would suggest to the customer to call to the local sales rep and request a site visit to evaluate.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:31 PM

0 Likes
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:31 PM

Hi,

It sounds more like the sales team than the engineering team.

To clarify, I want to know what I need to make this work, once I have that information, I will be able to determine if my office/building can support that infrastructure.

Thanks,

--Pete

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:31 PM

0 Likes
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:31 PM

Pete,

While I understand what the question is, noone that moderates the APC Discussion page, nor Tech Support can provide you with that information. You need to have a manufacturer's representative come to your site and view what the system's current capabilities are, and a build-out should be done AFTER that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:30 PM

0 Likes
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:30 PM

Hmm,

OK, what if I rephrase the question.

I am interested in the APC InRow RC air conditioning units. Can anyone tell me what else is required to run such units?

Thanks,

--Pete

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:30 PM

0 Likes
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:11 AM . Last Modified: ‎2024-02-14 10:30 PM

Hi
From my point of view I would look through the document http://www.apcmedia.com/salestools/ASTE-6Z5S8Z_R1_EN.pdf
especially page 5.
This should help to understand how to remove hot and what the configuration could be.

Reply

Link copied. Please paste this link to share this article on your social media post.

kzmfarhang
kzmfarhang
Cadet

Posted: ‎2024-04-24 03:43 AM

0 Likes
0
1027
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-24 03:43 AM

HI dear, which are system of cooling for our new data center under designed? our data center are 220 rack with 3 MW power. DX cooling with this part number ACRD301S is suitable for us ? or it is better we choose chilled water system?  

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore