Checking Smart-UPS ability to charge

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Checking Smart-UPS ability to charge
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:41 AM . Last Modified: ‎2024-03-15 06:15 AM

0 Likes
3
1611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:41 AM . Last Modified: ‎2024-03-15 06:15 AM

Checking Smart-UPS ability to charge

Greetings.

I picked up a used Smart-UPS 1500 Tower (SMT1500 - Feb 2011) for next to nothing at a thrift store.  As I expected, the LCD panel indicates that the battery pack is the original and that they need to be replaced.  No power on errors are shown other than to replace the battery.  

To perform a simple test to verify that the UPS is indeed charging, what voltage should I expect to see on a meter at the plug going to the battery with the UPS on and the battery disconnected?  I would like to get a warmer-fuzzier feeling for the UPS health before laying out the money for a new battery.

Thanks in advance.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
older_apc
Crewman older_apc
Crewman

Posted: ‎2021-06-28 09:41 AM . Last Modified: ‎2024-03-15 06:15 AM

0 Likes
0
1611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:41 AM . Last Modified: ‎2024-03-15 06:15 AM

Hi Stewart
First, check the fuse F900 and R792 on the charger board. 
The module is located on a separate charge behind the battery compartment.
If you have skills in working with electronics, you can turn it on on the table from a laboratory source or sequentially 
through a lamp. The power connector AC J901 pins 1, 3.
DC can measure pins 1 (+ DC) on connector J906; 8 (-Common). 
Check whether the IC900 TNY280GN chip is visually destroyed.
The destruction of resistors R758, R759, R760, R762 is not excluded.
Vladimir

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:41 AM . Last Modified: ‎2024-03-15 06:15 AM

0 Likes
0
1611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:41 AM . Last Modified: ‎2024-03-15 06:15 AM

Hi Stewart,

The charging voltage you should measure on the internal battery connector with the UPS on and the battery disconnected is around 27VDC for the SMT1500.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:41 AM . Last Modified: ‎2024-03-15 06:15 AM

0 Likes
0
1611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:41 AM . Last Modified: ‎2024-03-15 06:15 AM

Hi Szabi,

Thank you for the posting the charging voltage.  Sadly, I see 0 VDC (zero volts) on the battery connector with the battery connected and the UPS turned on.  That would tell me that the UPS is not going to charge the battery.  I'm very glad to know this now before I spent the money on a new battery.

Thanks again for the feedback.

Stewart

Reply

Link copied. Please paste this link to share this article on your social media post.

older_apc
Crewman older_apc
Crewman

Posted: ‎2021-06-28 09:41 AM . Last Modified: ‎2024-03-15 06:15 AM

0 Likes
0
1612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:41 AM . Last Modified: ‎2024-03-15 06:15 AM

Hi Stewart
First, check the fuse F900 and R792 on the charger board. 
The module is located on a separate charge behind the battery compartment.
If you have skills in working with electronics, you can turn it on on the table from a laboratory source or sequentially 
through a lamp. The power connector AC J901 pins 1, 3.
DC can measure pins 1 (+ DC) on connector J906; 8 (-Common). 
Check whether the IC900 TNY280GN chip is visually destroyed.
The destruction of resistors R758, R759, R760, R762 is not excluded.
Vladimir
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore