Charger Fault & PFC Fault on MGE Galaxy 5000 80KVA

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Charger Fault & PFC Fault on MGE Galaxy 5000 80KVA
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

0 Likes
4
5144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

Charger Fault & PFC Fault on MGE Galaxy 5000 80KVA

Hi Team,

We facing a problem on MGE Galaxy 5000 80KVA. the UPS mimic panel indicated "Charger Fault" & "PFC Fault".

As the DCHON board was already replaced we tried to upgrade the control kit (MIZEN, CHAN, GDEN) by a higher technical level kit, but the fault occurred after three days.

Then we exchanged the two MUTON boards to see if there is a faulty in PFC board ( if there is a fault the UPS will indicate "Inverter Fault" instead of "PFC Fault"), but the UPS indicated "Charger Fault" & "PFC Fault" again.

Next step we replaced the (DCHON Ventilation Fan), and this was a most successful stage as the UPS indicated "PFC Fault" after about 2 weeks without "Charger Fault".

Finally, we re installed the old control version but the UPS indicated "Internal CAN Communication Fault" beside "Charger Fault" & "PFC Fault".

Could you please share your experience in this case?

Thanks


Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

0 Likes
0
5144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

It appears this issue could be many different things and may require a service provider to resolve. The response I received was fairly detailed and seemed to indicate only service personnel should take care of this.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

0 Likes
0
5144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

I am looking into a reply to help you with this one. 3 phase MGE is not my thing unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

0 Likes
0
5144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

hai ahmed

checked the u are battery bank ,mostly u are battery one or more open 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

0 Likes
0
5145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

It appears this issue could be many different things and may require a service provider to resolve. The response I received was fairly detailed and seemed to indicate only service personnel should take care of this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:56 AM . Last Modified: ‎2024-03-19 12:28 AM

0 Likes
0
5144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:56 AM . Last Modified: ‎2024-03-19 12:28 AM

thanks Angela for your appreciated reply.

@weragala: we have already checked the batteries, however thank you for counseling smile

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore