Changing Network Gateway IP Address and NMCs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Changing Network Gateway IP Address and NMCs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:51 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
11
2587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:51 AM . Last Modified: ‎2024-03-05 10:45 PM

Changing Network Gateway IP Address and NMCs

Hi.

As you will be able to tell from the question, I am not completely up to speed on networking.  I recently changed my ISP from DSL to a cable and the IP address of my modem router has changed from 192.168.1.1 to 192.168.0.1.  So I guess this means the gateway has changed among other things.  I can no longer see my three NMCs and wonder what the best way , i.e. easiest way, to reconfigure them so that they can be seen on the new network.  The IP addresses of the three NMCs were manually configured as well.  I can still go back to the old network configuration if necessary.

Thanks in advance for any information you can give!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
0
2587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

What color is the one on the right (next to the checkmark and X)? Like orange and green alternating, just orange, etc? It should be solid green if its configured with an IP but the fact that it is flashing means its doing something else.

Since it is doing something else, using our Device IP Config Wizard software to find it on your home network may work.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:51 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
0
2587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:51 AM . Last Modified: ‎2024-03-05 10:45 PM

Hi.

As you will be able to tell from the question, I am not completely up to speed on networking.  I recently changed my ISP from DSL to a cable and the IP address of my modem router has changed from 192.168.1.1 to 192.168.0.1.  So I guess this means the gateway has changed among other things.  I can no longer see my three NMCs and wonder what the best way , i.e. easiest way, to reconfigure them so that they can be seen on the new network.  The IP addresses of the three NMCs were manually configured as well.  I can still go back to the old network configuration if necessary.

Thanks in advance for any information you can give!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:51 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
0
2587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:51 AM . Last Modified: ‎2024-03-05 10:45 PM

Hi Joe,

With manually assigned addresses, I believe on the UPSs you have, you can update via the LCD on the UPSs (for SMX/SMT). I believe you need to have the menus in Advanced Mode and its under Configuration when they are in Advanced. You'll need to change the third octet on both IP address and gateway (the 1 to a 0) to match your network's scheme. You should be able to just use the up and down arrows and tell it to change the IPs and gateways.

If this does not work, the serial cable might be the easiest to get out and log in and change it since the device IP wizard we offer, can only find items on the same network as your computer you run it on and now you're on a different network. (192.168.0.1 vs. 192.168.1.1).

Alternatively, you can just change the IP scheme on your new router's range to match the management cards as you mentioned which might be quicker if you can access your router now.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:51 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
0
2587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:51 AM . Last Modified: ‎2024-03-05 10:45 PM

Hi Angela,

I took your advice and used the front panel to configure the NMC2s in the SMT3000 and the SMX1500RM2U even though the smart bet was, as you mentioned, changing the router's IP scheme.  I haven't done the NMC in the old SU2200 but, I suspect, I will have to log in via the cable and do it from there.  Thanks much!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:51 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
0
2587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:51 AM . Last Modified: ‎2024-03-05 10:45 PM

You're welcome. And yes, with the SU2200, I'd just use the cable OR do a direct connection with a crossover ethernet cable from your computer to the NMC and set up your computer to the old scheme of 192.168.1.X and then type the NMC's IP in the web browser to access it, change the IP settings to the new scheme, let it reboot, then switch your computer back to the settings previously and you should be able to access it as well.

If you need help doing that, let me know what operating system you have on a computer you connect with.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
0
2587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

Thanks for the suggestion on the crossover cable.  I'll build one to take care of the SU2200.  Ciao!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
0
2587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

Also, if your computer's NIC is gigabit (1000mpbs) capable, it will auto-crossover for you with a regular straight through cable.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
0
2588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

What color is the one on the right (next to the checkmark and X)? Like orange and green alternating, just orange, etc? It should be solid green if its configured with an IP but the fact that it is flashing means its doing something else.

Since it is doing something else, using our Device IP Config Wizard software to find it on your home network may work.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
0
2587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

I am not having much luck getting the AP9617 talking to me.  I tried connecting my laptop with a gigabit NIC directly to the NMC and got nothing.  I tried both a straight thru and a newly made crossover cable.  The two lights on the AP9617 are both flashing.  The one on the left looking at the back of  the unit appears to be illuminating at a random rate.  The light on the right is cycling on and off at about a 1 second interval.and is very rythmic in nature.  The NIC on the laptop has one solid orange light and one is turning on and off at a random rate.  Of course I cannot find my old serial cable.  I also went back to the old network who's gateway wsa 192.168.1.1 and couldn't reach the UPS either.  Any other thoughts?  Thank you Angela.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
0
2587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

The one with the "X" is orange and flashing cyclically on and off.  I wonder what I did to it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
0
2587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

OK, that means its trying to do a BOOTP request (which your router probably just supports DHCP). I would try running our device IP configuration Wizard software to see if its able to find the device since you don't have your cable handy. (you can get it from here -> http://www.apc.com/tools/download/index.cfm and filter by software/firmware and choose software upgrades - wizards and configurators).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

0 Likes
0
2587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:52 AM . Last Modified: ‎2024-03-05 10:45 PM

Great minds think alike!  I just completed it and it found the unconfigured NMC.  The utility restored it to service.  I wonder why it became unconfigured?  Woohoo!!!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore