Hi All,
Is there a possibility to adjust the changeover time?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:58 PM . Last Modified: 2024-03-07 01:41 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:58 PM . Last Modified: 2024-03-07 01:42 AM
Hi Tharindu,
What changeover time are you referring?
What unit are you referring?
Kindest Regards,
Rich…
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:58 PM . Last Modified: 2024-03-07 01:42 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:58 PM . Last Modified: 2024-03-07 01:42 AM
Dear Richard,
this is regarding APC ATS 7723.
on this unit, can we change the transfer time?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:58 PM . Last Modified: 2024-03-07 01:42 AM
Hi Tharindu,
The transfer time is typically 8-12 ms and cannot be configured.
Further information can be found in the technical brochure below:
http://www.apc.com/salestools/THON-7GTPY6/THON-7GTPY6_R5_EN.pdf
Kindest Regards,
Rich…
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:58 PM . Last Modified: 2024-03-07 01:41 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:58 PM . Last Modified: 2024-03-07 01:41 AM
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.