Cannot log on to APC Management Web Server

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Cannot log on to APC Management Web Server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:46 AM

0 Likes
4
20510
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:46 AM

Cannot log on to APC Management Web Server

I am managing two UPS systems that are connected to our network via LAN connection cards.  Until recently, I was able to access them both by entering their IP addresses into a browser window, and then entering the (default) credentials into the login screen.  However, for the last few weeks, one of those is returning an error when I enter these credentials, saying "Someone is currently logged into the APC Management Web Server. Please try again later."  This has been going on for some weeks now, during which time all the servers that may have had a session open from their consoles - have been rebooted.  My PC, which would be the most obvious access point, has also been rebooted (many many times), and whenever I have had a session open, it very quickly times out anyway - so I am at a loss as to how this is happening.  Other than actually shutting down the UPS (which I really don't want to do, for obvious reasons), I can't think of a way to either identify where the open session is being held, or to force it off or bypass it.  Does anyone have any ideas?

Thanks

Graham

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
0
20505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:45 AM

Same right back at ya!

Thanks again.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:46 AM

0 Likes
0
20505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:46 AM

Hi Graham,

Immediate solutions to regain access:

 - pull the network management card out and re-insert, or insert a paperclip into the reset hole.

 - set SNMP OID .1.3.6.1.4.1.318.2.2.1.0 to 1

When you have access to the web, you might check control->security->session managment to see if any sessions stay active longer than you expect. Also under configuration->security->session management be sure to allow concurrent logins.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:46 AM

0 Likes
0
20505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:46 AM

Many thanks voidstar - so the answer turned out to be as simple as straightening a paper clip smile after I had spent a month or so looking for 'technical' solutions.  It worked perfectly... thank you so much.  I can't see the Control->Security setting options you mentioned, but now I am armed with this swiss army knife tool - I feel totally invincible and don't care if anyone else locks the session again - I can get around it and kick them off...

Thanks again

Graham

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
0
20505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:45 AM

Great! Happy holidays, and enjoy the swiss army paper clip.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
0
20506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:45 AM

Same right back at ya!

Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore