Cannot log into AP9605 card

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Cannot log into AP9605 card
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

0 Likes
32
6062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

Cannot log into AP9605 card

I've received a SU700RMNET that had an AP9605 installed. I've reset the unit, used a correct cable...but it is not accepting the apc/apc username and password. Is there another way to reset the root account information?

I know it is only an SNMP card, but that's all I'm looking to use it as.

Message was edited by: cernst

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:42 AM

0 Likes
0
6062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:42 AM

That worked great. Thank you very much. I was not doing it within the time limit. How something so simple can turn...

Thanks again.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 32
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

0 Likes
0
6060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

well, not sure if it was what you helped me with, but I had taken the card out and set it on my desk over the weekend. I put it back in today, I tried the backdoor and it didn't login with it. Just for giggles, I tried apc/apc...and it worked. I don't know if it was because it sat w/o power for an extended time that completely reset it...but it works now. thanks for the help!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

0 Likes
0
6060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

as promised, here they are based on the serial numbers you provided:

A95066606540 is *****

WA9633324837 is *****

WA9739201893 is *****

WA9808641714 is *****

WA9802476743 is *****

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

0 Likes
0
6060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

i will get you these tomorrow, sorry for the delay.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

0 Likes
0
6060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

Jolyf,

The backdoor password for serial number WA9807628417 is: ***** (the character after the ^ is a capital I as in "India").

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

0 Likes
0
6061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

that one would be ******

just a reminder, this backdoor password resets the password to apc/apc. so you log in with apc/backdoor password then that resets it to apc/apc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

0 Likes
0
6061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

can you generate password for my card?
s/n: WA9838467464

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

0 Likes
0
6061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:26 PM . Last Modified: ‎2024-03-15 02:44 AM

hi - it is *****

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:44 AM

0 Likes
0
6061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:44 AM

thanks, but i saw strange behavior of card. my original login was apc and when i typed login and backdoor password i was promted for login again (like i enter wrong login and password), but after that try to enter default login apc with default password apc and login was successful. :-).... and all work fine. but for assurance i change login and password after that

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:44 AM

0 Likes
0
6061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:44 AM

Great, I would like to restore the family!

Can you provide me the password for:

A95066606540
WA9633324837
WA9739201893
WA9808641714
WA9802476743

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:44 AM

0 Likes
0
6061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:44 AM

that one is 1357>=^IBC;C

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

from now on, i am going to request that anyone needing a backdoor password preferably contact APC support via phone or email (800-890-4272 or esupport@apcc.com) or worst case, Private Message me so I can get you the password via PM.

thanks. i am going to lock the thread so that no more requests can be submitted on this post.

i also edited out all of the passwords that were present in this thread.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

Can you generate password for my cards:
ZA0534009561
JS0537023882

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

these cards dont have a backdoor password because they are too new i think, based on the serial number. can you confirm what model they are and what devices they are embedded in and i will confirm.

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

I am also having this same problem, but with an AP9617 Management Card.
apc/apc is not working and reset button does not help.

I was woundering if you could create a password for JA0322008902.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

I get a permission denied on the linked procedure.

It does have a reset button, the card does seem to be rebooting...but the apc/apc does not work.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

i have the manual, which ill just attach incase you ever need it but does it have a reset button it? i dont have one handy right this second..

you can try [this procedure noted here|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=77]

no promises on that though but its a start..maybe someone else can chime in.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

Corey,

The AP9605 may require a backdoor password in conjunction with the prior user name to obtain backdoor access.

If you know the original username, and can provide the serial number for the card, I can possibly post a backdoor password generated here.

I cannot guarantee at this time that this is the correct solution though. However, I will continue to research. For the time being, it is worth a shot.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

Serial number is WA9838467672
I do not know what the previous username/password was...it may not have been changed from apc/apc

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

Try apc for the usernam and ****** for the password. In the IBB string it is the letter "eye".

If that's not it, chances are it was changed from the default apc/apc as you stated it's not letting you in, but here's the manual for the AP9605 in case you want to double check your settings.


My mistake, Angela already provided the manual.

Message was edited by: The Notorious K.M.P.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

I'm having the same problem. Could you send me the back door code for this SN: WA9825150490 It is also an AP9605.
The reset mode doesn't seem to work with this one.

Thanks
Nick

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

Hello,
The age of the cards ( looking at the serial number) is more then 10years!
I assume that something happened to EEPROM memory, internal chips (ICs) and I would not waste time here with it... Just to use new one....modern one

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

Nick,

Go ahead and try the admin username, then ***** for the password, then apc/apc to get in. If this doesn't work, I would try the reset procedure again, this time waiting a few seconds in between each time you press the reset button.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

Thanks

That did it. I'm in. And yes, I should get a newer card... I should get a new ups too. (MX5000XR) 🙂

Thanks Again

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:27 PM . Last Modified: ‎2024-03-15 02:43 AM

Please if possible generate one for me also, as I have exactly same problem.
Unfortunely iv got 3 cards:
WA9830007063
WA9847017460
WA9826000006

Alos apc/apc is not working and reset button doesn't helping.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:43 AM

WA9830007063 *****
WA9847017460 *****
WA9826000006 *****

I recommend pasting those password strings into notepad or into a text editor using a single spaced font. Arial/Helvetica makes it very difficult to distinguish capital I from lowercase L, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:43 AM

I have another card to get a password:
S/N: WA9838467000

...please


edit:
if I change the serial number to the one in my original problem, with the generated pw work in this 2nd card? In other words, are these passwords linked to the NMC's serial number?

Message was edited by: cernst

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:43 AM

yes, they are linked.

***** is for serial number of WA9838467000.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:43 AM

I am also having this same problem with my AP9605 Management Card.
apc/apc is not working and reset button does not help.

I was woundering if you could create a password for WA9808639363.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:43 AM

Hello,

I’m lost with an AP9605 password for s/n WA9807628417

Can you provide me the backdoor code?

Cordially

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:43 AM

0 Likes
0
6060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:43 AM

Hello,
I have a AP9210 with the serial of WA9907012397
can you get me a password?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:42 AM

0 Likes
0
6061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:42 AM

There is no backdoor password for AP9617's, other than going through the reset procedure.

When doing the reset procedure, after pressing the reset button the first time, wait for the lights to alternately flash. Then press it a second time, and the lights will go out. As soon as the lights go out, press Enter in Hyperterminal, until you receive a username prompt. From that point, you have 15 seconds before it times out.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:42 AM

0 Likes
0
6063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:28 PM . Last Modified: ‎2024-03-15 02:42 AM

That worked great. Thank you very much. I was not doing it within the time limit. How something so simple can turn...

Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.