Cannot email

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Cannot email
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:13 AM

0 Likes
5
2858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:13 AM

Cannot email

Does anyone know why I cannot send email from my new, well, refurbished, APC Smart-UPS 1400? I have a AP9617 APC UPS Network Management Card installed and apparently running fine. One of the reasons I got this was to get email when some condition arose, but I cannot get either email or DNS to work.

I have tried sending email using an IP address as well as a domain name, but as I cannot get the domain server test to work, I thought the IP address used for the email would work. It does not.

The log gives me "Systems: Email: could not email 'lawrence.hare@[ip address]'"

The IP address is the email server I use for my normal outgoing email.

When I run a DNS test I get "The DNS server was unable to process query." This response come back immediately, there is no delay, so I do not think it is even trying!

I have the router IP and everything configured.

What am I missing?

Thanks - Lawrence Hare

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

Yes, you have confirmed my worst fears. I do not have a local emailer and was relying on the thing smtp'ing to one of my mail agents outside the local network, I thought it could speak 821 and handle 822, that is what I got from the documentation. Yes, port 25 is blocked, I verified it. I need to use a dedicated port and use it with authentication. So I am indeed stuck.

Well, I should have spent more time downloading the manual and reading it thoroughly.

Very, but very, annoying.

Down the road I shall be installing a Mac Mini Server to take over DHCP and implement a more flexible firewall with vpn support and all. I can set up a mail server on the thing and have it relay.

Still and all.

Ruined my evening.

Thanks for the help.

Lawrence

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

In regards to the DNS test issue by itself...the cards use the standard DNS port, 53, for DNS communication and I've frankly never heard of anyone who had an issue with DNS because port 53 was blocked, but I suppose it's possible.

Well, what I meant about authentication was in regards to SMTP authentication, i.e. a user name and password being required to allow inbound/outbound mail requests. In terms of the SMTP network port the card uses, yes it defaults to port 25, and there is no way to make it use a different port.

The NMC2 cards (AP9630, AP9631) are the current generation of network cards for our UPS systems, and they do support basic SMTP authentication (user name, password). However, you still cannot change the network port that they use for SMTP.

I haven't heard of a lot of NIC-type devices running their own onboard SMTP/Mail server...and no the card would not communicate to any APC e-mail server. The card only sends SMTP requests and traffic to the SMTP server defined in the E-mail Settings section.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

Are you sure you have confirmed the proper mail server? It sounds like you have, but try using an nslookup on the e-mail domain suffix using type=mx. You should use the result that has the lowest "mx" value. Also confirm that your TCP/IP settings are absolutely correct, and that your DNS servers are set correctly. If you put the card on the same network subnet as some other computer that works with DNS and e-mail, and match its relevant "ipconfig/all" settings, the e-mail should work unless there is some firewall rule blocking ports/IP of the card specifically. Also, make sure the "from address" in the e-mail settings exactly matches the format needed to match the e-mail domain you use, and make sure there are no rules preventing the card from sending out e-mails at the address you specify. Additionally, note that the NMC card you have does not support e-mail authentication.

Try moving it to another location on the network if all this fails, also update/reinstall the newest version of the "SUMX" type firmware to the card, and if all else fails try rebooting the card "to defaults" using the option in the GUI (under the Administration section if you have relatively recent firmware).

I know that sounds like stuff you have confirmed but it is fairly often that some minor detail was the crux of the problem. If all this does not work you may need to call into tech. support @ 1-800-800-4272 for more detailed assistance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

Suddenly I am very concerned! Thank you for your reply. I am almost certain Verizon blocks port 25, and with no authentication I cannot access the others I have on different ports as they all require authentication.

And the ENTIRE master plan of taking this route was that this UPS supports emailing of events.

I had thought that APC used its own email server which did not require authentication for outgoing messages, but if that uses port 25 I am stuck and if they do not, then I have no where to go with this.

I just suddenly have a very unhappy feeling that all this work has been for nothing.

Do other cards support authentication? Yet I saw no other card other than those with environmental monitoring (9618, 9619). I purchased this from a refurbishing company and this was the only NMS card I saw. It never occurred to me that it might not provide the features needed to actually work. This is bad.

Any thoughts?

Thanks - Lawrence

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

keep in mind, you need to be on the network of where your email server resides. you cannot use the network management card to send email using something like smtp.gmail.com unless you have an email server in your network set to relay mail to smtp.gmail.com or something external which builds upon the type=mx nslookup stuff that erasmus already mentioned.

if you want to use gmail, you need to be on the gmail network, if you want to use yahoo, you need to be on the yahoo network, etc

essentially, you need to use a local SMTP (email) server.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

0 Likes
0
2858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:54 PM . Last Modified: ‎2024-03-14 01:12 AM

Yes, you have confirmed my worst fears. I do not have a local emailer and was relying on the thing smtp'ing to one of my mail agents outside the local network, I thought it could speak 821 and handle 822, that is what I got from the documentation. Yes, port 25 is blocked, I verified it. I need to use a dedicated port and use it with authentication. So I am indeed stuck.

Well, I should have spent more time downloading the manual and reading it thoroughly.

Very, but very, annoying.

Down the road I shall be installing a Mac Mini Server to take over DHCP and implement a more flexible firewall with vpn support and all. I can set up a mail server on the thing and have it relay.

Still and all.

Ruined my evening.

Thanks for the help.

Lawrence

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore