Can you copy local user accounts across multiple UPS and PDU NMCs?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can you copy local user accounts across multiple UPS and PDU NMCs?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
5
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

Can you copy local user accounts across multiple UPS and PDU NMCs?

I am working on bulk configuration of multiple UPS and PDU's wtih NMC's (Mostly NMC2 AP9631 units) I am using the technique of downloading, editing and uploading config.ini files across them, but the config.ini file does not appear to contain local user account information. It there a way to bulk copy user accounts too? (I don't want to use a RADIUS server for this as those might shut down as and when the power goes out.)

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
0
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

I am working on bulk configuration of multiple UPS and PDU's wtih NMC's (Mostly NMC2 AP9631 units) I am using the technique of downloading, editing and uploading config.ini files across them, but the config.ini file does not appear to contain local user account information. It there a way to bulk copy user accounts too? (I don't want to use a RADIUS server for this as those might shut down as and when the power goes out.)

Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
0
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

For NMC2 (AP9630/31) v5.X.X firmware, you'll only find local usernames in the config.ini. Passwords are not stored for security reasons but you can add a keyword to the file and upload it still to do a bulk change. But, if you download the config.ini after the change, you won't see the new password for the reason I just mentioned.

For NMC2 v6.X.X and higher, we now support a multiple user system. You won't find any usernames in config.ini anymore. For bulk changes, creations of new users, etc, you can use a new .csf file type which is basically a script that utilizes the user CLI command syntax. So, you can use that file to bulk add users, adjust passwords, change user preferences, etc. To assist with a default template to make the .csf file easier to deal with if many of your users have the same preferences, you can set up default settings in the web UI or with usrdflt command (I think thats how you spell it anyway off the top of my head - to view all commands, you can type ? or help at the CLI via local console, telnet or SSH.) The only way you can currently view your users is in the interface itself (you can't really download a list in a .txt file direct from the card). In the web, you can find the current user list and click on individual users. In the CLI, you can do user -l to see the current users and their permissions and if they are enabled or disabled.

So I think the thought process here is make a .csf file (just a plain text file that you change the extension for) and type out the commands to add the users/passwords/preferences you'd like and you can upload it just like a config.ini. I believe viewing the current "database" of local users via a file output is no longer an option and I was told for security reasons - now you can only view it by logging into the interface.

Let me know if you have any questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
0
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

Thanks, I'm running v6.0.6 FW so I can use the second method you suggest. Where can I find the proper documentation for this feature?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
0
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

Now that you mention it, I can't find anything public - how helpful huh? embarassed I will put it on my list of knowledge bases I need to create but for now, here is a little bit of information below from trainings I provide to our technical support teams. If you have more questions or need further detail before I get that knowledge base done (hopefully in the next week), then I'll be happy to walk through it with you.

Users can now be added via a CLI script file (.csf) which a user can create using a plain text editor, such as Notepad. It must only contain one command per line. This file can be uploaded to the NMC via FTP/SCP.

It utilizes the same syntax as the user command in the CLI:

Usage: user --  Configuration Options

    user -n

                   [-cp  ] (Req. For Super User Account)

                   [-pw  ]

                   [-pe  ]

                          (user permission)

                   [-d   ]

                   [-e   ] (Access Enable)

                   [-st  ] minute(s)

                   [-sr  ] (Serial Remote Auth. Override)

                   [-el  ] (Event Log Color Coding)

                   [-lf  ] (Export Log Format)

                   [-ts  ] (Temperature Scale)

                   [-df 

                          dd-mmm-yy | yyyy-mm-dd>] (Date Format)

                   [-lg  ] (User Language)

                   [-del ]

                   [-l   (shows current user list)]

Example:


user -n newadmin -pw apc -pe administrator -e enable

user -n newdevice -pw apc -pe device -lg enUs -e enable

user -n newdev1 -pw dv1 -pe device -e enable

...Before I forget, I think there is a bug and adding read only via the CLI no matter this way or manually doesn't work properly. It would need to be done via the web. The rest of the user types should work. We fixed this for the next release.

If all your users will have similar settings, here is the User Default Settings you could set/review prior so you don't have to adjust them for every user. Again, this should serve as a template and these are configurable via config.ini which you could do first, then set up your users. Then you only need to change the settings for users that are not using the stuff in the standard template.

Usage: userdflt --  Configuration Options

    userdflt [-e   ] (Enable)

             [-pe  ]

                    (user permission)

             [-d   ]

             [-st  ] minute(s)

             [-bl  ]

             [-el  ] (Event Log Color Coding)

             [-lf  ] (Export Log Format)

             [-ts  ] (Temperature Scale)

             [-df 

                    dd-mmm-yy | yyyy-mm-dd>] (Date Format)

             [-lg  ] (User Language)

             [-sp  ] (Strong Passwords)

             [-pp  ] (Required Password Change Interval)

I was thinking this would be the foundation of my knowledge base article I can make for our users. Do you have questions/comments I can help with that I should also include in the article?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
0
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

OK, I'll try and implement it and let you know if I have any comments. I have some other questions about user accounts that I am going to post separately before I do this.

Thanks,

Daniel.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
0
2055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

I am working on bulk configuration of multiple UPS and PDU's wtih NMC's (Mostly NMC2 AP9631 units) I am using the technique of downloading, editing and uploading config.ini files across them, but the config.ini file does not appear to contain local user account information. It there a way to bulk copy user accounts too? (I don't want to use a RADIUS server for this as those might shut down as and when the power goes out.)

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore