AP9631 reboots when I try to set Alert settings.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9631 reboots when I try to set Alert settings.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
jmakowski_apc
Crewman jmakowski_apc
Crewman

Posted: ‎2021-07-01 04:42 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
5
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:42 AM . Last Modified: ‎2024-03-05 01:59 AM

AP9631 reboots when I try to set Alert settings.


I have 2 AP9631's, each in a Smart-UPS RT 3000 XL.  I have many other Smart-UPS RT 3000 XL units with AP9631's in them.  Yet these two (in our Oakland office) are the only ones that do this.

If I try to set Alert settings, either "By Group" or "By Event", the minute I click Apply the AP9631 reboots.  When it comes back up, the Alert(s) I tried to change is(are) back to the original configuration.

It seems odd to me that only these two units would have this issue.  Perhaps it is a problem with the batch these two AP9631's came from?

Has anyone else seen this before?

I am adding the Dump and Debug files from the device.   The Dump lists the cause as a Heap Reset.  I tried reloading the Firmware/Software on one of them but it did not resolve the issue.  The Firmware/Software image is the same exact file installed on the other devices.

They are running:

Application Module
Name:sumx
Version:v6.0.6
Date:Apr  5 2013
Time:11:25:39
APC OS (AOS)
Name:aos
Version:v6.0.6
Date:Apr  5 2013
Time:10:36:37
APC Boot Monitor
Name:bootmon
Version:v1.0.2
Date:Jan 21 2010
Time:13:35:57

This is identical to other units not experiencing this.

Any help is appreciated.

Thanks,

Jim Makowski

Attachments
dump.txt.zip
CA1 debug.txt.zip
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

It's likely, if anything, it's a firmware bug. What we are finding is there seems to be a memory issue which could be due to your particular configuration.

If it were me, what I'd suggest we can is a "format" (but that will wipe every single setting on the network management card, including IP settings), so if you can't do that via the format command in telnet/SSH/local console, the next best is to reset to defaults excluding TCP/IP settings so you can still log in and not lose the IP settings. With a minimal configuration, such as JUST your email server/recipient settings, I'd try it again to see if it still does this when you try to change configuration settings. Then, we slowly configure it to see if we can narrow down what in your configuration is possibly causing this. I have done this set up a few times and it does not occur so I don't think it is affecting everyone.

If anything has changed since you gave me this config.ini, you could also back up your config.ini again so once we get this sorted, you have a back up file to load at least.

Let me know if you have any questions prior to moving forward or need clarification. We just need to narrow down the problem area to determine where there is a bug or issue.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:42 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:42 AM . Last Modified: ‎2024-03-05 01:59 AM

I do not see the same TCP/IP stack failure I was expecting to see. I'll need to have someone look at these further and report back. It could still be related to the issue we've seen with the uncached mail server but maybe presenting itself in a different way.

Oh, I forgot - can you get me config.ini's from these units or at least one and one that's working properly? I know you said you had identical units that were not doing this.

Reply

Link copied. Please paste this link to share this article on your social media post.

jmakowski_apc
Crewman jmakowski_apc
Crewman

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM


I have 2 AP9631's, each in a Smart-UPS RT 3000 XL.  I have many other Smart-UPS RT 3000 XL units with AP9631's in them.  Yet these two (in our Oakland office) are the only ones that do this.

If I try to set Alert settings, either "By Group" or "By Event", the minute I click Apply the AP9631 reboots.  When it comes back up, the Alert(s) I tried to change is(are) back to the original configuration.

It seems odd to me that only these two units would have this issue.  Perhaps it is a problem with the batch these two AP9631's came from?

Has anyone else seen this before?

I am adding the Dump and Debug files from the device.   The Dump lists the cause as a Heap Reset.  I tried reloading the Firmware/Software on one of them but it did not resolve the issue.  The Firmware/Software image is the same exact file installed on the other devices.

They are running:

Application Module
Name:sumx
Version:v6.0.6
Date:Apr  5 2013
Time:11:25:39
APC OS (AOS)
Name:aos
Version:v6.0.6
Date:Apr  5 2013
Time:10:36:37
APC Boot Monitor
Name:bootmon
Version:v1.0.2
Date:Jan 21 2010
Time:13:35:57

This is identical to other units not experiencing this.

Any help is appreciated.

Thanks,

Jim Makowski

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

Can you please give event.txt too?

Reply

Link copied. Please paste this link to share this article on your social media post.

jmakowski_apc
Crewman jmakowski_apc
Crewman

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

Here is a config.ini from one of the units in our Cambridge office.

Attachments
10.4.3.12.ini.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

0 Likes
0
1450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:43 AM . Last Modified: ‎2024-03-05 01:59 AM

It's likely, if anything, it's a firmware bug. What we are finding is there seems to be a memory issue which could be due to your particular configuration.

If it were me, what I'd suggest we can is a "format" (but that will wipe every single setting on the network management card, including IP settings), so if you can't do that via the format command in telnet/SSH/local console, the next best is to reset to defaults excluding TCP/IP settings so you can still log in and not lose the IP settings. With a minimal configuration, such as JUST your email server/recipient settings, I'd try it again to see if it still does this when you try to change configuration settings. Then, we slowly configure it to see if we can narrow down what in your configuration is possibly causing this. I have done this set up a few times and it does not occur so I don't think it is affecting everyone.

If anything has changed since you gave me this config.ini, you could also back up your config.ini again so once we get this sorted, you have a back up file to load at least.

Let me know if you have any questions prior to moving forward or need clarification. We just need to narrow down the problem area to determine where there is a bug or issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore