Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Can a messed up battery constant cause premature self-test failure ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can a messed up battery constant cause premature self-test failure ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:53 PM . Last Modified: ‎2024-03-14 03:55 AM

0 Likes
2
1194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:53 PM . Last Modified: ‎2024-03-14 03:55 AM

Can a messed up battery constant cause premature self-test failure ?

The question really is, what variables does an APC smart-ups processor look at when determining when it is time to replace batteries ? Is the ups able to determine the internal resistance (impedance) of the battery string and monitor for increases in impedance caused by aging ? Or does it only look at the discharging voltage/current when on battery during the self test? Does it use the value for the battery constant in any way ? IE if the batttery constant is messed up could the batteries be flagged bad prematurely during a self-test ?

I have been replacing a lot of batteries lately that are only 3 years old, and doing post-mortem testing on individual cells in the strings with my B & K tester shows the impedance of the battery has not risen that significantly - Eg I just pulled a tray of eight 12V/7.2 AH cells out of an SUA3000 , and each of the cells measured between 0.140 and 0.150 ohms versus 0.100 ohms for a brand new cell.

Are there any actual APC ups engineering staff listening to this forum that can enlighten me / us ?

Thanks,
Dave
Univ of BC
Canada

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 10:53 PM . Last Modified: ‎2024-03-14 03:55 AM

0 Likes
0
1194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:53 PM . Last Modified: ‎2024-03-14 03:55 AM

The problem with measuring resistance in an battery is that you have to simultaniously put a load on it while reading this measurement for acurate readings on battery health. Batteries internal impedances are read better read with a meter that can accuratly measure into micro ohms while applying a load(alber cell corder). So from what you just said a new battery has an internal impedance of 100K uohms and a flagged battery has around 140K-150K uohms. Thats a 50% increase in internal impedance. You will not see a very high impedance before the battery can no longer properly hold a charge and supply current during an outage. You would never see 1 or 2 actual ohms on a battery, or should I say a properly working battery.

To increase you life on your batteries I would reduce the self test frequency from 7 days to 60 or 90 days. The less you discharge your batteries the longer they will last. Also watch your server room temperature and where the UPS is placed. A standard rule of thumb for batteries is that there life is reduced by half for every 10 degree's f over 77.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:53 PM . Last Modified: ‎2024-03-14 03:55 AM

0 Likes
0
1194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:53 PM . Last Modified: ‎2024-03-14 03:55 AM

i dont know the details but the the self-test process compares the battery voltage during a discharge to an internal bad-battery template – basically, it places a load on the battery and measures the voltage drop. If the drop is too large for the given load, then the voltage will be beneath the failure level and the self-test will fail, thus illuminating the replace battery LED.

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 10:53 PM . Last Modified: ‎2024-03-14 03:55 AM

0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:53 PM . Last Modified: ‎2024-03-14 03:55 AM

The problem with measuring resistance in an battery is that you have to simultaniously put a load on it while reading this measurement for acurate readings on battery health. Batteries internal impedances are read better read with a meter that can accuratly measure into micro ohms while applying a load(alber cell corder). So from what you just said a new battery has an internal impedance of 100K uohms and a flagged battery has around 140K-150K uohms. Thats a 50% increase in internal impedance. You will not see a very high impedance before the battery can no longer properly hold a charge and supply current during an outage. You would never see 1 or 2 actual ohms on a battery, or should I say a properly working battery.

To increase you life on your batteries I would reduce the self test frequency from 7 days to 60 or 90 days. The less you discharge your batteries the longer they will last. Also watch your server room temperature and where the UPS is placed. A standard rule of thumb for batteries is that there life is reduced by half for every 10 degree's f over 77.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore